Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa09606;
          3 Jan 94 13:15 EST
Received: from CNRI.RESTON.VA.US by IETF.CNRI.Reston.VA.US id aa09602;
          3 Jan 94 13:15 EST
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa19185; 3 Jan 94 13:15 EST
Received: from localhost by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id NAA04272; Mon, 3 Jan 1994 13:01:38 -0500
X-Resent-To: ups-mib@CS.UTK.EDU ; Mon, 3 Jan 1994 13:01:36 EST
Errors-to: owner-ups-mib@CS.UTK.EDU
Received: from dub-img-2.compuserve.com by CS.UTK.EDU with ESMTP (8.6.4/2.8s-UTK)
	id NAA04247; Mon, 3 Jan 1994 13:01:33 -0500
Received: from localhost by dub-img-2.compuserve.com (8.6.4/5.930129sam)
	id NAA07748; Mon, 3 Jan 1994 13:01:03 -0500
Date: 03 Jan 94 12:55:19 EST
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: "Ron Pitt (NSSI)" <71303.577@compuserve.com>
To: UPSMIB <ups-mib@cs.utk.edu>
Subject: Re: The latest draft.
Message-ID: <940103175518_71303.577_DHQ89-1@CompuServe.COM>

I was under the impression that this review was to be for editorial 
mistakes only.  In that spirit, NSSI likes this draft and has no problem
with it going to the "Proposed Standard" phase.

I would be VERY MUCH AGAINST major changes at this point in the process.
This would include removal of a conformance group.

Ron Pitt
NSSI



Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa28298;
          4 Jan 94 0:37 EST
Received: from CNRI.RESTON.VA.US by IETF.CNRI.Reston.VA.US id aa28294;
          4 Jan 94 0:37 EST
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa12187; 4 Jan 94 0:37 EST
Received: from localhost by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id AAA19782; Tue, 4 Jan 1994 00:26:03 -0500
X-Resent-To: ups-mib@CS.UTK.EDU ; Tue, 4 Jan 1994 00:26:01 EST
Errors-to: owner-ups-mib@CS.UTK.EDU
Received: from arl-img-1.compuserve.com by CS.UTK.EDU with ESMTP (8.6.4/2.8s-UTK)
	id AAA19773; Tue, 4 Jan 1994 00:26:00 -0500
Received: from localhost by arl-img-1.compuserve.com (8.6.4/5.930129sam)
	id AAA01968; Tue, 4 Jan 1994 00:25:30 -0500
Date: 04 Jan 94 00:22:50 EST
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: "Terry L. Zumwalt" <71151.2550@compuserve.com>
To: UPS SNMP MIB Committe <UPS-MIB@cs.utk.edu>
Subject: IPM's Input
Message-ID: <940104052249_71151.2550_CHE68-1@CompuServe.COM>

IPM is also opposed to any 11th hour changes.  We agree completely with
NSSI on changes to the proposed draft.  We also have intentions of using
the Basic compliance group it should stay as agreed upon in Houston. 
Changes at this time should be minor.

Regards 

Terry L. Zumwalt
International Power Machines Corp.



Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa09242;
          6 Jan 94 13:10 EST
Received: from CNRI.RESTON.VA.US by IETF.CNRI.Reston.VA.US id aa09235;
          6 Jan 94 13:10 EST
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa14136; 6 Jan 94 13:10 EST
Received: from localhost by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id MAA14482; Thu, 6 Jan 1994 12:54:56 -0500
X-Resent-To: ups-mib@CS.UTK.EDU ; Thu, 6 Jan 1994 12:54:55 EST
Errors-to: owner-ups-mib@CS.UTK.EDU
Received: from nic.cerf.net by CS.UTK.EDU with ESMTP (8.6.4/2.8s-UTK)
	id MAA14471; Thu, 6 Jan 1994 12:54:53 -0500
Received: from localhost (rdraper@localhost) by nic.cerf.net (8.6.4/8.6.4) id JAA20160; Thu, 6 Jan 1994 09:55:42 -0800
Date: Thu, 6 Jan 1994 09:55:15 -0800 (PST)
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: "Roger W. Draper" <rdraper@cerf.net>
X-Orig-Sender: "Roger W. Draper" <rdraper@cerf.net>
Reply-To: "Roger W. Draper" <rdraper@cerf.net>
Subject: No New Changes
To: UPS-MIB Mailing list <ups-mib@cs.utk.edu>
Message-ID: <Pine.3.85.9401060946.A18311-0100000@nic.cerf.net>
MIME-Version: 1.0
Content-Type: TEXT/PLAIN; CHARSET=US-ASCII


Liebert Corporation is also opposed to any last minute changes to the
proposed standard, only editorial mistakes should be corrected at this
time.

Roger Draper
Liebert Corp.







Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa11700;
          6 Jan 94 14:23 EST
Received: from CNRI.RESTON.VA.US by IETF.CNRI.Reston.VA.US id aa11696;
          6 Jan 94 14:23 EST
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa16589; 6 Jan 94 14:23 EST
Received: from localhost by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id OAA20705; Thu, 6 Jan 1994 14:13:40 -0500
X-Resent-To: ups-mib@CS.UTK.EDU ; Thu, 6 Jan 1994 14:13:39 EST
Errors-to: owner-ups-mib@CS.UTK.EDU
Received: from relay2.UU.NET by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id OAA20697; Thu, 6 Jan 1994 14:13:37 -0500
Received: from spool.uu.net (via LOCALHOST) by relay2.UU.NET with SMTP 
	(5.61/UUNET-internet-primary) id AA11212; Thu, 6 Jan 94 14:13:29 -0500
Received: from apc.UUCP by uucp5.uu.net with UUCP/RMAIL
	(queueing-rmail) id 065832.13247; Thu, 6 Jan 1994 06:58:32 EST
Received: by apc (AIX 3.2/UCB 5.64/4.03)
          id AA19338; Wed, 5 Jan 1994 18:59:56 -0500
Date: Wed, 5 Jan 1994 18:59:56 -0500
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: Doug Rademacher <apc!dougr@uunet.uu.net>
Message-Id: <9401052359.AA19338@apc>
To: uunet!cs.utk.edu!ups-mib@uunet.uu.net
Subject: 11th hour changes

My most recent messages were written in reference to Jeff's list of issues
still outstanding.  I am only trying to address those issues.  My messages 
were also completed before Jeff's deadline of 12/29.  If we had wanted to stop
any more discussion, then there shouldn't have been a call for more input.  I 
was under the impression that we should make any changes now, because they 
would be very difficult to change later.

When, actually, is the 11th hour?  Is it now?  Is it 6 months from now?  

If the points I made were valid, then let's address them before it really is 
too late.  So far this forum has only heard from five participants.  Is every-
one still on vacation?

_____________________________________________________________________      
                              _  ___  ___ 
                             / \   _)/  
                            /  _\||  \___
--------------------------------------------------------------------- 
Douglas J. Rademacher             | American Power Conversion Corp. 
Director of Software Development  | 132 Fairgrounds Road
                                  | West Kingston, RI 02818
apc!dougr@uunet.uu.net            | (401) 789-5735 x2073
---------------------------------------------------------------------


Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa14437;
          9 Jan 94 12:30 EST
Received: from CNRI.RESTON.VA.US by IETF.CNRI.Reston.VA.US id aa14433;
          9 Jan 94 12:30 EST
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa25271; 9 Jan 94 12:30 EST
Received: from localhost by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id MAA21401; Sun, 9 Jan 1994 12:14:55 -0500
X-Resent-To: ups-mib@CS.UTK.EDU ; Sun, 9 Jan 1994 12:14:54 EST
Errors-to: owner-ups-mib@CS.UTK.EDU
Received: from vms.macc.wisc.edu by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id MAA21394; Sun, 9 Jan 1994 12:14:52 -0500
Received: from VMSmail by vms.macc.wisc.edu; Sun, 09 Jan 94 11:12 CDT
Message-Id: <24010911120350@vms.macc.wisc.edu>
Date: Sun, 09 Jan 94 11:12 CDT
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: Brian Young <BYOUNG@macc.wisc.edu>
Subject: My review
To: ups-mib@cs.utk.edu
X-VMS-To: in%"ups-mib@cs.utk.edu",BYOUNG

Hi guys,
Sorry for the long delay in getting my comments in. Just completed
reviewing all mail since the last release of the MIB. A few comments...
 
BEST would like to see the basic group remain. Our Fortress has many of the
features required for full-featured compliance, but not all, so it marries
better with the basic group. I think that many of us have units that fit
this category, but don't want to admit it for some reason. :)
 
BEST also hmmms on the killing of the config group variables: input voltage,
input frequency, output voltage, output frequency, output VA and output
power from the subset group!
 
We also feel that changes should be kept to a minimum at this point. Things
look pretty good right now, so let's keep it that way. I've got enough gray
hairs from this project already. :)
 
Regards,
Brian Young
Best Power Technology


Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa04655;
          10 Jan 94 12:26 EST
Received: from CNRI.RESTON.VA.US by IETF.CNRI.Reston.VA.US id aa04651;
          10 Jan 94 12:26 EST
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa17446; 10 Jan 94 12:26 EST
Received: from localhost by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id MAA02250; Mon, 10 Jan 1994 12:15:41 -0500
X-Resent-To: ups-mib@CS.UTK.EDU ; Mon, 10 Jan 1994 12:15:39 EST
Errors-to: owner-ups-mib@CS.UTK.EDU
Received: from dante.exide.com by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id MAA02237; Mon, 10 Jan 1994 12:15:38 -0500
Received: by dante.exide.com (5.0/1.34)
	id AA02185; Mon, 10 Jan 94 12:18:35 EST
Date: Mon, 10 Jan 94 12:18:35 EST
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: Tom Brennan <tom@dante.exide.com>
Message-Id: <9401101718.AA02185@dante.exide.com>
To: ups-mib@cs.utk.edu
Subject: When can we expect the Final draft of MIB?
Content-Length: 165

The deadline for comments is passed, and even the late comments
have slowed down to a trickle.
For our planning purposes, when can we expect to see the final draft?


Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa04594;
          19 Jan 94 11:28 EST
Received: from CNRI.RESTON.VA.US by IETF.CNRI.Reston.VA.US id aa04590;
          19 Jan 94 11:28 EST
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa08922; 19 Jan 94 11:28 EST
Received: from localhost by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id JAA02612; Wed, 19 Jan 1994 09:45:52 -0500
X-Resent-To: ups-mib@CS.UTK.EDU ; Wed, 19 Jan 1994 09:45:50 EST
Errors-to: owner-ups-mib@CS.UTK.EDU
Received: from sun4nl.NL.net by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id JAA02579; Wed, 19 Jan 1994 09:45:36 -0500
Received: from vicnl by sun4nl.NL.net via EUnet
	id AA29996 (5.65b/CWI-3.3); Wed, 19 Jan 1994 15:45:34 +0100
Received: from vic1 by vicnl.victron.nl id aa08498; 19 Jan 94 14:53 CET
Received: from VICTRON_ONE/TEMPQ by vic1.victron.nl (Mercury 1.11);
    Wed, 19 Jan 94 14:58:56 CET
Received: from TEMPQ by VICTRON_ONE (Mercury 1.11); Wed, 19 Jan 94 14:58:40 CET
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: "Jack Stiekema, PE0MOT" <JACK@vic1.victron.nl>
Organization:  Victron bv 
To: ups-mib@cs.utk.edu
Date:          Wed, 19 Jan 1994 14:58:33 GMT+0200
Subject:       Re: When can we expect the Final draft of MIB?
Reply-To: jack@victron.nl
Priority: normal
X-Mailer:     PMail v3.0 (R1a)
Message-Id: <15429465D90@vic1.victron.nl>

it's quit,

what is the next date?


Kind regards,
Jack
+----------------------------------------------------+
| Victron bv   POB 31   9700 AA Groningen   Holland  |
|   phone: +31 50 446222   fax: +31 50 424107        |
+----------------------------------------------------+


Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa14993;
          19 Jan 94 19:02 EST
Received: from CNRI.RESTON.VA.US by IETF.CNRI.Reston.VA.US id aa14989;
          19 Jan 94 19:02 EST
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa20042; 19 Jan 94 19:02 EST
Received: from localhost by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id SAA12555; Wed, 19 Jan 1994 18:44:16 -0500
X-Resent-To: ups-mib@CS.UTK.EDU ; Wed, 19 Jan 1994 18:44:15 EST
Errors-to: owner-ups-mib@CS.UTK.EDU
Received: from relay1.UU.NET by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id SAA12546; Wed, 19 Jan 1994 18:44:10 -0500
Received: from spool.uu.net (via LOCALHOST) by relay1.UU.NET with SMTP 
	(5.61/UUNET-internet-primary) id AAvzow28356; Wed, 19 Jan 94 18:44:07 -0500
Received: from apc.UUCP by uucp5.uu.net with UUCP/RMAIL
	(queueing-rmail) id 154016.7038; Wed, 19 Jan 1994 15:40:16 EST
Received: by apc (AIX 3.2/UCB 5.64/4.03)
          id AA17652; Wed, 19 Jan 1994 11:14:17 -0500
Date: Wed, 19 Jan 1994 11:14:17 -0500
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: Doug Rademacher <apc!dougr@uunet.uu.net>
Message-Id: <9401191614.AA17652@apc>
To: uunet!cs.utk.edu!ups-mib@uunet.uu.net
Subject: ping


ping

_____________________________________________________________________      
                              _  ___  ___ 
                             / \   _)/  
                            /  _\||  \___
--------------------------------------------------------------------- 
Douglas J. Rademacher             | American Power Conversion Corp. 
Director of Software Development  | 132 Fairgrounds Road
                                  | West Kingston, RI 02818
apc!dougr@uunet.uu.net            | (401) 789-5735 x2073
---------------------------------------------------------------------


Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa00705;
          20 Jan 94 2:56 EST
Received: from CNRI.RESTON.VA.US by IETF.CNRI.Reston.VA.US id aa00701;
          20 Jan 94 2:56 EST
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa01499; 20 Jan 94 2:56 EST
Received: from localhost by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id CAA10827; Thu, 20 Jan 1994 02:45:26 -0500
X-Resent-To: ups-mib@CS.UTK.EDU ; Thu, 20 Jan 1994 02:45:25 EST
Errors-to: owner-ups-mib@CS.UTK.EDU
Received: from sun4nl.NL.net by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id CAA10811; Thu, 20 Jan 1994 02:45:22 -0500
Received: from vicnl by sun4nl.NL.net via EUnet
	id AA14006 (5.65b/CWI-3.3); Thu, 20 Jan 1994 08:45:23 +0100
Received: from vic1 by vicnl.victron.nl id aa09612; 20 Jan 94 8:13 CET
Received: from VICTRON_ONE/TEMPQ by vic1.victron.nl (Mercury 1.11);
    Thu, 20 Jan 94 8:19:11 CET
Received: from TEMPQ by VICTRON_ONE (Mercury 1.11); Thu, 20 Jan 94 8:18:57 CET
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: "Jack Stiekema, PE0MOT" <JACK@vic1.victron.nl>
Organization:  Victron bv 
To: ups-mib@cs.utk.edu
Date:          Thu, 20 Jan 1994 08:18:49 GMT+0200
Subject:       Re: When can we expect the Final draft of MIB?
Reply-To: jack@victron.nl
Priority: normal
X-Mailer:     PMail v3.0 (R1a)
Message-Id: <16580563E0A@vic1.victron.nl>

->it's quit,
->
->what is the next date?

Adam Stolinsky and i are afraid we in Europ missed the boat (or did it
sink?).

Ping looks ok Doug (or is it a submarine sonar).


Kind regards,
Jack
+----------------------------------------------------+
| Victron bv   POB 31   9700 AA Groningen   Holland  |
|   phone: +31 50 446222   fax: +31 50 424107        |
+----------------------------------------------------+


Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa20774;
          23 Jan 94 20:02 EST
Received: from CNRI.RESTON.VA.US by IETF.CNRI.Reston.VA.US id aa20770;
          23 Jan 94 20:02 EST
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa01265; 23 Jan 94 20:02 EST
Received: from localhost by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id TAA08214; Sun, 23 Jan 1994 19:52:43 -0500
X-Resent-To: ups-mib@CS.UTK.EDU ; Sun, 23 Jan 1994 19:52:41 EST
Errors-to: owner-ups-mib@CS.UTK.EDU
Received: from relay1.UU.NET by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id TAA08182; Sun, 23 Jan 1994 19:52:36 -0500
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: yamai@soliton.co.jp
MMDF-Warning:  Parse error in original version of preceding line at CNRI.Reston.VA.US
Received: from spool.uu.net (via LOCALHOST) by relay1.UU.NET with SMTP 
	(5.61/UUNET-internet-primary) id AAwadv05014; Sun, 23 Jan 94 19:52:38 -0500
Received: from iij.UUCP by uucp6.uu.net with UUCP/RMAIL
	(queueing-rmail) id 195142.13026; Sun, 23 Jan 1994 19:51:42 EST
Received: from localhost by uucp0.iij.ad.jp (8.6.5+2.3W/2.7W)
	id JAA05910; Mon, 24 Jan 1994 09:42:29 +0900
Received: by brahma.soliton.co.jp (4.1/IIJ-U1.1)
	id AA11271; Mon, 24 Jan 94 09:40:19 JST
Date: Mon, 24 Jan 94 09:40:19 JST
Message-Id: <9401240040.AA11271@brahma.soliton.co.jp>
To: ups-mib@cs.utk.edu
Subject: Please send me the UPS MIB or document.

Hello.
This is M.Yamai.

I am Engnir. of Soliton Systems K.K. Japan.
I plan to develop first UPS agent in Japan.
But I  have no information about UPS MIB or UPS agent.
Please send me the USP MIB or UPS agents information.

Regard.

 /yamai@soliton.co.jp


Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa25325;
          23 Jan 94 23:06 EST
Received: from CNRI.RESTON.VA.US by IETF.CNRI.Reston.VA.US id aa25321;
          23 Jan 94 23:06 EST
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa03757; 23 Jan 94 23:06 EST
Received: from localhost by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id WAA19695; Sun, 23 Jan 1994 22:56:57 -0500
X-Resent-To: ups-mib@CS.UTK.EDU ; Sun, 23 Jan 1994 22:56:55 EST
Errors-to: owner-ups-mib@CS.UTK.EDU
Received: from UTKVX3.UTK.EDU by CS.UTK.EDU with ESMTP (8.6.4/2.8s-UTK)
	id WAA19678; Sun, 23 Jan 1994 22:56:54 -0500
Received: from utkvx.utk.edu by utkvx.utk.edu (PMDF V4.2-13 #4157) id
 <01H81EU6NVXS8Y53EH@utkvx.utk.edu>; Sun, 23 Jan 1994 22:56:46 EST
Date: Sun, 23 Jan 1994 22:56:46 -0500 (EST)
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: CASE@utkvx.utcc.utk.edu
Subject: status
To: ups-mib@cs.utk.edu
Message-id: <01H81EU6QAQQ8Y53EH@utkvx.utk.edu>
X-VMS-To: IN%"ups-mib@cs.utk.edu"
X-VMS-Cc: CASE
MIME-version: 1.0
Content-type: TEXT/PLAIN; CHARSET=US-ASCII
Content-transfer-encoding: 7BIT

the reviews conducted by the snmp directorate are now completed and
i am incorporating their comments and input from the list into the
document at this time

regards,
jdc


Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa29958;
          24 Jan 94 3:16 EST
Received: from CNRI.RESTON.VA.US by IETF.CNRI.Reston.VA.US id aa29954;
          24 Jan 94 3:16 EST
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa07401; 24 Jan 94 3:16 EST
Received: from localhost by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id DAA04443; Mon, 24 Jan 1994 03:06:36 -0500
X-Resent-To: ups-mib@CS.UTK.EDU ; Mon, 24 Jan 1994 03:06:35 EST
Errors-to: owner-ups-mib@CS.UTK.EDU
Received: from sun4nl.NL.net by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id DAA04436; Mon, 24 Jan 1994 03:06:29 -0500
Received: from vicnl by sun4nl.NL.net via EUnet
	id AA26777 (5.65b/CWI-3.3); Mon, 24 Jan 1994 09:06:31 +0100
Received: from vic1 by vicnl.victron.nl id aa15967; 24 Jan 94 8:45 CET
Received: from VICTRON_ONE/TEMPQ by vic1.victron.nl (Mercury 1.11);
    Mon, 24 Jan 94 8:49:41 CET
Received: from TEMPQ by VICTRON_ONE (Mercury 1.11); Mon, 24 Jan 94 8:49:30 CET
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: "Jack Stiekema, PE0MOT" <JACK@vic1.victron.nl>
Organization:  Victron bv 
To: ups-mib@cs.utk.edu
Date:          Mon, 24 Jan 1994 08:49:22 GMT+0200
Subject:       IETF meeting ??
Reply-To: jack@victron.nl
Priority: normal
X-Mailer:     PMail v3.0 (R1a)
Message-Id: <44079E4E54@vic1.victron.nl>

Do we attend the IETF meeting end March in Seatle?

Please a concensus a.s.a.p. because of my overfilled agenda.


Kind regards,
Jack
+----------------------------------------------------+
| Victron bv   POB 31   9700 AA Groningen   Holland  |
|   phone: +31 50 446222   fax: +31 50 424107        |
+----------------------------------------------------+


Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa07942;
          24 Jan 94 11:26 EST
Received: from CNRI.RESTON.VA.US by IETF.CNRI.Reston.VA.US id aa07938;
          24 Jan 94 11:26 EST
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa16843; 24 Jan 94 11:26 EST
Received: from localhost by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id LAA11300; Mon, 24 Jan 1994 11:13:59 -0500
X-Resent-To: ups-mib@CS.UTK.EDU ; Mon, 24 Jan 1994 11:13:57 EST
Errors-to: owner-ups-mib@CS.UTK.EDU
Received: from metronet.com by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id LAA11293; Mon, 24 Jan 1994 11:13:55 -0500
Received: by metronet.com id AA09317
  (5.67a/IDA1.5hp for UPS-MIB@CS.UTK.EDU); Mon, 24 Jan 1994 10:14:04 -0600
Date: Mon, 24 Jan 1994 10:13:05 -0500 (CDT)
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: Greg Hanka <ghanka@metronet.com>
X-Orig-Sender: Greg Hanka <ghanka@metronet.com>
Reply-To: Greg Hanka <ghanka@metronet.com>
Subject: Ground fault/no ground alarms
To: UPS-MIB@cs.utk.edu
Message-Id: <Pine.3.87.9401241012.A9054-0100000@feenix.metronet.com>
Mime-Version: 1.0
Content-Type: TEXT/PLAIN; CHARSET=US-ASCII


Cris Buck, UPS Prod. Mgr. at EFI Electronics, asked me why the very
important "ground fault/no ground" conditions are not enumerated
specifically as an alarm or alarms.  It is his belief that these are
very important items and I presume many would concur.  It is my
recollection that these were discussed along with other input items and
the consensus was that they all fell into the category of the alarm
UPSALARMINPUTBAD.  Can someone please enlighten me on the issue and
discussion of ground fault handling?

Better Regards,
Go Cowboys/Chiefs

Gordon Monk
via Greg Hanka, ghanka@metronet.com

+--------------------------------------------------------------------------+
Gregory M. Hanka                                             P.O. Box 940148
Director of Software Development                        Plano, TX 75094-0148
Net X, Inc., Dallas, TX. 
Internet:   ghanka@metronet.com                               / Public key \
Compu$erve: 72223,172  (72223.172@compuserve.com)             \ via finger /
+--------------------------------------------------------------------------+





Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa01085;
          25 Jan 94 6:54 EST
Received: from CNRI.RESTON.VA.US by IETF.CNRI.Reston.VA.US id ai01032;
          25 Jan 94 6:54 EST
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa01408; 25 Jan 94 5:30 EST
Received: from localhost by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id CAA15410; Tue, 25 Jan 1994 02:15:22 -0500
X-Resent-To: ups-mib@CS.UTK.EDU ; Tue, 25 Jan 1994 02:15:21 EST
Errors-to: owner-ups-mib@CS.UTK.EDU
Received: from sun4nl.NL.net by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id CAA15401; Tue, 25 Jan 1994 02:15:19 -0500
Received: from vicnl by sun4nl.NL.net via EUnet
	id AA12221 (5.65b/CWI-3.3); Tue, 25 Jan 1994 08:15:20 +0100
Received: from vic1 by vicnl.victron.nl id aa17797; 25 Jan 94 8:08 CET
Received: from VICTRON_ONE/TEMPQ by vic1.victron.nl (Mercury 1.11);
    Tue, 25 Jan 94 8:13:23 CET
Received: from TEMPQ by VICTRON_ONE (Mercury 1.11); Tue, 25 Jan 94 8:13:12 CET
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: "Jack Stiekema, PE0MOT" <JACK@vic1.victron.nl>
Organization:  Victron bv 
To: ups-mib@cs.utk.edu, ghanka@metronet.com
Date:          Tue, 25 Jan 1994 08:13:09 GMT+0200
Subject:       Re: Ground fault/no ground alarms
Reply-To: jack@victron.nl
Priority: normal
X-Mailer:     PMail v3.0 (R1a)
Message-Id: <5B6D652D65@vic1.victron.nl>

->Date sent:      Mon, 24 Jan 1994 10:13:05 -0500 (CDT)
->From:           Greg Hanka <ghanka@metronet.com>
->Subject:        Ground fault/no ground alarms
->Cris Buck, UPS Prod. Mgr. at EFI Electronics, asked me why the very
->important "ground fault/no ground" conditions are not enumerated
->specifically as an alarm or alarms.  It is his belief that these are
->Gordon Monk

Hi Gordon,

I did a ctrlqfind on all email but there is no "ground" mentioned last
10 months except for Doug's address, so sri. Maybe we mentioned it in
Dallas?


Kind regards,
Jack
+----------------------------------------------------+
| Victron bv   POB 31   9700 AA Groningen   Holland  |
|   phone: +31 50 446222   fax: +31 50 424107        |
+----------------------------------------------------+


Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa03292;
          25 Jan 94 10:46 EST
Received: from CNRI.RESTON.VA.US by IETF.CNRI.Reston.VA.US id aa03288;
          25 Jan 94 10:46 EST
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa01167; 25 Jan 94 8:45 EST
Received: from localhost by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id IAA15272; Tue, 25 Jan 1994 08:24:14 -0500
X-Resent-To: ups-mib@CS.UTK.EDU ; Tue, 25 Jan 1994 08:24:14 EST
Errors-to: owner-ups-mib@CS.UTK.EDU
Received: from dante.exide.com by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id IAA15265; Tue, 25 Jan 1994 08:24:12 -0500
Received: by dante.exide.com (5.0/1.34)
	id AA16243; Tue, 25 Jan 94 08:27:29 EST
Date: Tue, 25 Jan 94 08:27:29 EST
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: Tom Brennan <tom@dante.exide.com>
Message-Id: <9401251327.AA16243@dante.exide.com>
To: ups-mib@cs.utk.edu
Subject: re: Ground fault

My memory is not to be fully trusted, but this is what I recall:
on the assumption that most such wiring problems are installation
rather than on going problems (eg, phase rotation), and from
the point of view of the network manager (well, what more can
he do but have somebody sent out to check the "Bad Input Line"),
we refrained from adding more specific alarms for bad input.
Too infrequent, not manageable (remember snM!p).

Tom Brennan, Exide


Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa05676;
          25 Jan 94 12:34 EST
Received: from CNRI.RESTON.VA.US by IETF.CNRI.Reston.VA.US id aa05630;
          25 Jan 94 12:34 EST
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa06991; 25 Jan 94 12:34 EST
Received: from localhost by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id MAA02793; Tue, 25 Jan 1994 12:02:10 -0500
X-Resent-To: ups-mib@CS.UTK.EDU ; Tue, 25 Jan 1994 12:02:06 EST
Errors-to: owner-ups-mib@CS.UTK.EDU
Received: from LOCALHOST by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id MAA02737; Tue, 25 Jan 1994 12:01:49 -0500
Message-Id: <199401251701.MAA02737@CS.UTK.EDU>
To: yamai@soliton.co.jp
cc: ups-mib@cs.utk.edu
Subject: Re: Please send me the UPS MIB or document. 
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: Ken Key <ups-mib-request@cs.utk.edu>
In-reply-to: Your message of Mon, 24 Jan 1994 09:40:19 +0200.
             <9401240040.AA11271@brahma.soliton.co.jp> 
Date: Tue, 25 Jan 1994 12:01:43 -0500
X-Orig-Sender: key@cs.utk.edu

Greetings,
   Here is a copy of the latest draft of the IETF UPS MIB Working Group
Internet Draft.   There will be a new draft in the next few weeks, but
the changes should be mostly editorial.  You can subscribe to the UPS MIB
Working Group e-mailing list by sending a request to:

    ups-mib-request@cs.utk.edu


The UPS MIB is 56 pages long.



--
Ken Key (ups-mib-request@cs.utk.edu)
Univ. of Tennessee, Knoxville

=============================================================================





          draft                        UPS MIB                 December 1993


                           UPS Management Information Base

                                    December 1993


                           Jeffrey D. Case, Ph.D. (Editor)
                             SNMP Research, Incorporated
                                    case@snmp.com


                              <draft-ietf-upsmib-03.txt>


                                 Status of this Memo

          This document is an Internet Draft.  Internet Drafts are working
          documents of the Internet Engineering Task Force (IETF), its
          Areas, and its Working Groups.  Note that other groups may also
          distribute working documents as Internet Drafts.

          Internet Drafts are valid for a maximum of six months and may be
          updated, replaced, or obsoleted by other documents at any time.
          It is inappropriate to use Internet Drafts as reference material
          or to cite them other than as a "work in progress".


























          Expires June 1994                                         [Page 1]





          draft                        UPS MIB                 December 1993


          1.  Introduction

          This memo defines an experimental portion of the Management
          Information Base (MIB) for use with network management protocols
          in the Internet community.  In particular, it defines objects for
          managing uninterruptible power supply (UPS) systems.












































          Expires June 1994                                         [Page 2]





          draft                        UPS MIB                 December 1993


          2.  The SNMPv2 Network Management Framework

          The SNMPv2 Network Management Framework consists of four major
          components.  They are:

          o    RFC 1442 which defines the SMI, the mechanisms used for
               describing and naming objects for the purpose of management.

          o    RFC 1213 defines MIB-II, the core set of managed objects for
               the Internet suite of protocols.

          o    RFC 1445 which defines the administrative and other
               architectural aspects of the framework.

          o    RFC 1448 which defines the protocol used for network access
               to managed objects.

          The Framework permits new objects to be defined for the purpose of
          experimentation and evaluation.


          2.1.  Object Definitions

          Managed objects are accessed via a virtual information store,
          termed the Management Information Base or MIB.  Objects in the MIB
          are defined using the subset of Abstract Syntax Notation One
          (ASN.1) defined in the SMI.  In particular, each object type is
          named by an OBJECT IDENTIFIER, an administratively assigned name.
          The object type together with an object instance serves to
          uniquely identify a specific instantiation of the object.  For
          human convenience, we often use a textual string, termed the
          descriptor, to refer to the object type.


















          Expires June 1994                                         [Page 3]





          draft                        UPS MIB                 December 1993


          3.  Overview

          This document defines the managed objects for Uninterruptible
          Power Supplies which are to be manageable via the Simple Network
          Management Protocol (SNMP).


          4.  Status

          YET TO BE DONE:
          1.  Proofread carefully by multiple readers
          2.  Shorten some overly long lines






































          Expires June 1994                                         [Page 4]





          draft                        UPS MIB                 December 1993


          5.  Definitions

          UPS-MIB DEFINITIONS ::= BEGIN

          IMPORTS
              MODULE-IDENTITY, OBJECT-TYPE, NOTIFICATION-TYPE,
              OBJECT-IDENTITY, experimental, Counter32, Gauge32, Integer32    |
                  FROM SNMPv2-SMI
              DisplayString, TimeStamp, TestAndIncr                           |
                  FROM SNMPv2-TC
              MODULE-COMPLIANCE, OBJECT-GROUP
                  FROM SNMPv2-CONF;


          upsMIB MODULE-IDENTITY
              LAST-UPDATED "9312210000Z"                                      |
              ORGANIZATION "IETF UPS MIB Working Group"
              CONTACT-INFO
                      "  Jeffrey D. Case (Editor)
                         SNMP Research, Incorporated
                         3001 Kimberlin Heights Road, Knoxville, TN, 37920
                         615-573-1434
                         case@snmp.com"

              DESCRIPTION
                      "The MIB module to describe Uninterruptible Power
                      Supplies."
              ::= { experimental 39 12 6 }                                    |

          PositiveInteger ::= TEXTUAL-CONVENTION
              DISPLAY-HINT "1d"
              STATUS       current
              DESCRIPTION
                      "This data type is a non-zero and non-negative value."
              SYNTAX       INTEGER (1..2147483648)

          NonNegativeInteger ::= TEXTUAL-CONVENTION
              DISPLAY-HINT "1d"
              STATUS       current
              DESCRIPTION
                      "This data type is a non-negative value."
              SYNTAX       INTEGER (0..2147483648)








          Expires June 1994                                         [Page 5]





          draft                        UPS MIB                 December 1993


          univPowerSupply       OBJECT IDENTIFIER ::= { experimental 39 }
          -- Note:  this should be unintPowerSupply

          upsMibDraft2          OBJECT IDENTIFIER ::= { univPowerSupply 12 }
          -- Note: univPowerSupply 1-12 were used in earlier drafts.
          -- From now on, drafts will use version and subversion numbers
          -- under the experimental tree to prevent OID name-space collision
          -- when implementing different versions of experimental MIBS.

          upsMibE26             OBJECT IDENTIFIER ::= { upsMibDraft2 6 }      |
          -- Experimental Version 2 minor version 6 (Exp v2.6) of UPS MIB.    |

          upsObjects            OBJECT IDENTIFIER ::= { upsMibE26 1 }         |


          --
          -- The Device Identification group.
          --      All objects in this group except for upsIdentName and
          --      upsIdentAttachedDevices are set at device initialization
          --      and remain static.
          --

          upsIdent              OBJECT IDENTIFIER ::= { upsObjects 1 }

          upsIdentManufacturer OBJECT-TYPE
              SYNTAX     DisplayString (SIZE (0..31))
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The name of the UPS manufacturer."
              ::= { upsIdent 1 }

          upsIdentModel OBJECT-TYPE
              SYNTAX     DisplayString (SIZE (0..63))
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The UPS Model designation."
              ::= { upsIdent 2 }

          upsIdentUPSSoftwareVersion OBJECT-TYPE
              SYNTAX     DisplayString (SIZE (0..63))
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION





          Expires June 1994                                         [Page 6]





          draft                        UPS MIB                 December 1993


                      "The UPS firmware/software version(s).  This variable
                      may or may not have the same value as
                      upsIdentAgentSoftwareVersion in some implementations."
              ::= { upsIdent 3 }

          upsIdentAgentSoftwareVersion OBJECT-TYPE
              SYNTAX     DisplayString (SIZE (0..63))
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The UPS agent software version.  This variable may or
                      may not have the same value as
                      upsIdentUPSSoftwareVersion in some implementations."
              ::= { upsIdent 4 }

          upsIdentName OBJECT-TYPE
              SYNTAX     DisplayString (SIZE(0..63))
              MAX-ACCESS read-write
              STATUS     current
              DESCRIPTION
                      "A string identifying the UPS.  This object should be
                      set by the administrator."
              ::= { upsIdent 5 }

          upsIdentAttachedDevices OBJECT-TYPE
              SYNTAX     DisplayString (SIZE(0..63))
              MAX-ACCESS read-write
              STATUS     current
              DESCRIPTION
                      "A string identifying the devices attached to the
                      output(s) of the UPS.  This object should be set by
                      the administrator."
              ::= { upsIdent 6 }

















          Expires June 1994                                         [Page 7]





          draft                        UPS MIB                 December 1993


          --
          -- Battery Group
          --

          upsBattery            OBJECT IDENTIFIER ::= { upsObjects 2 }

          upsBatteryStatus OBJECT-TYPE
              SYNTAX     INTEGER {
                  unknown(1),
                  batteryNormal(2),
                  batteryLow(3),
                  batteryDepleted(4)
              }
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The indication of the capacity remaining in the UPS
                      system's batteries.   A value of batteryNormal
                      indicates that the remaining run-time is greater than   |
                      upsConfigLowBattTime.                                   |
                      A value of batteryLow indicates that the remaining
                      battery run-time is less than or equal to               |
                      upsConfigLowBattTime.  A value of batteryDepleted       |
                      indicates that the UPS will be unable to sustain the
                      present load when and if the utility power is lost
                      (including the possibility that the utility power is
                      currently absent and the UPS is unable to sustain the
                      output)."
              ::= { upsBattery 1 }

          upsSecondsOnBattery OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "seconds"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "If the unit is on battery power, the elapsed time
                      since the UPS last switched to battery power, or the
                      time since the network management subsystem was last
                      restarted, whichever is less.  Zero shall be returned
                      if the unit is not on battery power."
              ::= { upsBattery 2 }

          upsEstimatedMinutesRemaining OBJECT-TYPE
              SYNTAX     PositiveInteger





          Expires June 1994                                         [Page 8]





          draft                        UPS MIB                 December 1993


              UNITS      "minutes"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "An estimate of the time to battery charge depletion
                      under the present load conditions if the utility power
                      were to be lost and remain off."
              ::= { upsBattery 3 }

          upsEstimatedChargeRemaining OBJECT-TYPE
              SYNTAX     INTEGER (0..100)
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "An estimate of the battery charge remaining expressed
                      as a percent of full charge."
              ::= { upsBattery 4 }

          upsBatteryVoltage OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "0.1 Volt DC"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The magnitude of the present battery voltage."
              ::= { upsBattery 5 }

          upsBatteryCurrent OBJECT-TYPE
              SYNTAX     Integer32                                            |
              UNITS      "0.1 Amp DC"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The present battery current."
              ::= { upsBattery 6 }

          upsBatteryTemperature OBJECT-TYPE
              SYNTAX     Integer32                                            |
              UNITS      "degrees Centigrade"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The ambient temperature at or near the UPS Battery
                      casing."
              ::= { upsBattery 7 }





          Expires June 1994                                         [Page 9]





          draft                        UPS MIB                 December 1993


          --
          -- Input Group
          --

          upsInput              OBJECT IDENTIFIER ::= { upsObjects 3 }

          upsInputFrequency OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "0.1 Hertz"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The present input frequency."
              ::= { upsInput 1 }

          upsInputLineBads OBJECT-TYPE
              SYNTAX     Counter32
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "A count of the number of times the input entered an
                      out-of-tolerance condition as defined by the
                      manufacturer."
              ::= { upsInput 2 }


          upsInputNumLines OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The number of input lines utilized in this device.
                      This variable indicates the number of rows in the
                      input table."
              ::= { upsInput 3 }

          upsInputTable OBJECT-TYPE
              SYNTAX     SEQUENCE OF UpsInputEntry
              MAX-ACCESS not-accessible
              STATUS     current
              DESCRIPTION
                      "A list of input table entries.  The number of entries
                      is given by the value of upsInputNumLines."
              ::= { upsInput 4 }






          Expires June 1994                                        [Page 10]





          draft                        UPS MIB                 December 1993


          upsInputEntry OBJECT-TYPE
              SYNTAX     UpsInputEntry
              MAX-ACCESS not-accessible
              STATUS     current
              DESCRIPTION
                      "An entry containing information applicable to a
                      particular input line."
              INDEX { upsInputLineIndex }
              ::= { upsInputTable 1 }

          UpsInputEntry ::= SEQUENCE {
              upsInputLineIndex   PositiveInteger,
              upsInputVoltage     NonNegativeInteger,
              upsInputCurrent     NonNegativeInteger,
              upsInputTruePower   NonNegativeInteger                          |
          }

          upsInputLineIndex OBJECT-TYPE
              SYNTAX     PositiveInteger
              MAX-ACCESS not-accessible
              STATUS     current
              DESCRIPTION
                      "The input line identifier."
              ::= { upsInputEntry 1 }

          upsInputVoltage OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "RMS Volts"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The magnitude of the present input voltage."
              ::= { upsInputEntry 2 }

          upsInputCurrent OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "0.1 RMS Amp"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The magnitude of the present input current."
              ::= { upsInputEntry 3 }

          upsInputTruePower OBJECT-TYPE                                       |
              SYNTAX     NonNegativeInteger





          Expires June 1994                                        [Page 11]





          draft                        UPS MIB                 December 1993


              UNITS      "Watts"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The magnitude of the present input true power."
              ::= { upsInputEntry 4 }












































          Expires June 1994                                        [Page 12]





          draft                        UPS MIB                 December 1993


          --
          -- The Output group.
          --

          upsOutput             OBJECT IDENTIFIER ::= { upsObjects 4 }

          upsOutputSource OBJECT-TYPE
              SYNTAX     INTEGER {
                  other(1),
                  none(2),                                                    |
                  normal(3),                                                  |
                  bypass(4),                                                  |
                  battery(5),                                                 |
                  booster(6),                                                 |
                  reducer(7)                                                  |
              }
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The present source of output power.  The enumeration   |
                      none(2) indicates that there is no source of output     |
                      power (and therefore no output power), for example,     |
                      the system has opened the output breaker."              |
              ::= { upsOutput 1 }

          upsOutputFrequency OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "0.1 Hertz"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The present output frequency."
              ::= { upsOutput 2 }

          upsOutputNumLines OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The number of output lines utilized in this device.
                      This variable indicates the number of rows in the
                      output table."
              ::= { upsOutput 3 }

          upsOutputTable OBJECT-TYPE





          Expires June 1994                                        [Page 13]





          draft                        UPS MIB                 December 1993


              SYNTAX     SEQUENCE OF UpsOutputEntry
              MAX-ACCESS not-accessible
              STATUS     current
              DESCRIPTION
                      "A list of output table entries.  The number of
                      entries is given by the value of upsOutputNumLines."
              ::= { upsOutput 4 }

          upsOutputEntry OBJECT-TYPE
              SYNTAX     UpsOutputEntry
              MAX-ACCESS not-accessible
              STATUS     current
              DESCRIPTION
                      "An entry containing information applicable to a
                      particular output line."
              INDEX { upsOutputLineIndex }
              ::= { upsOutputTable 1 }

          UpsOutputEntry ::= SEQUENCE {
              upsOutputLineIndex   PositiveInteger,
              upsOutputVoltage     NonNegativeInteger,
              upsOutputCurrent     NonNegativeInteger,
              upsOutputPower       NonNegativeInteger,
              upsOutputPercentLoad NonNegativeInteger
          }

          upsOutputLineIndex OBJECT-TYPE
              SYNTAX     PositiveInteger
              MAX-ACCESS not-accessible
              STATUS     current
              DESCRIPTION
                      "The output line identifier."
              ::= { upsOutputEntry 1 }

          upsOutputVoltage OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "RMS Volts"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The present output voltage."
              ::= { upsOutputEntry 2 }

          upsOutputCurrent OBJECT-TYPE
              SYNTAX     NonNegativeInteger





          Expires June 1994                                        [Page 14]





          draft                        UPS MIB                 December 1993


              UNITS      "0.1 RMS Amp"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The present output current."
              ::= { upsOutputEntry 3 }

          upsOutputPower OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "Watts"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The present output true power."
              ::= { upsOutputEntry 4 }

          upsOutputPercentLoad OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "percent"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The percentage of the UPS power capacity presently
                      being used, i.e., the greater of the percent load of
                      true power capacity and the percent load of VA."
              ::= { upsOutputEntry 5 }
























          Expires June 1994                                        [Page 15]





          draft                        UPS MIB                 December 1993


          --
          -- The Bypass group.
          --

          upsBypass             OBJECT IDENTIFIER ::= { upsObjects 5 }

          upsBypassFrequency OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "0.1 Hertz"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The present bypass frequency."
              ::= { upsBypass 1 }

          upsBypassNumLines OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The number of bypass lines utilized in this device.
                      This entry indicates the number of rows in the bypass
                      table."
              ::= { upsBypass 2 }

          upsBypassTable OBJECT-TYPE
              SYNTAX     SEQUENCE OF UpsBypassEntry
              MAX-ACCESS not-accessible
              STATUS     current
              DESCRIPTION
                      "A list of bypass table entries.  The number of
                      entries is given by the value of upsBypassNumLines."
              ::= { upsBypass 3 }

          upsBypassEntry OBJECT-TYPE
              SYNTAX     UpsBypassEntry
              MAX-ACCESS not-accessible
              STATUS     current
              DESCRIPTION
                      "An entry containing information applicable to a
                      particular bypass input."
              INDEX { upsBypassLineIndex }
              ::= { upsBypassTable 1 }

          UpsBypassEntry ::= SEQUENCE {





          Expires June 1994                                        [Page 16]





          draft                        UPS MIB                 December 1993


              upsBypassLineIndex  PositiveInteger,
              upsBypassVoltage    NonNegativeInteger,
              upsBypassCurrent    NonNegativeInteger,
              upsBypassPower      NonNegativeInteger
          }

          upsBypassLineIndex OBJECT-TYPE
              SYNTAX     PositiveInteger
              MAX-ACCESS not-accessible
              STATUS     current
              DESCRIPTION
                      "The bypass line identifier."
              ::= { upsBypassEntry 1 }

          upsBypassVoltage OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "RMS Volts"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The present bypass voltage."
              ::= { upsBypassEntry 2 }

          upsBypassCurrent OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "0.1 RMS Amp"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The present bypass current."
              ::= { upsBypassEntry 3 }

          upsBypassPower OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "Watts"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The present true power conveyed by the bypass."
              ::= { upsBypassEntry 4 }










          Expires June 1994                                        [Page 17]





          draft                        UPS MIB                 December 1993


          --
          -- The Alarm group.
          --

          upsAlarm              OBJECT IDENTIFIER ::= { upsObjects 6 }

          upsAlarmsPresent OBJECT-TYPE
              SYNTAX     Gauge32
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The present number of active alarm conditions."
              ::= { upsAlarm 1 }

          upsAlarmTable OBJECT-TYPE
              SYNTAX     SEQUENCE OF UpsAlarmEntry
              MAX-ACCESS not-accessible
              STATUS     current
              DESCRIPTION
                      "A list of alarm table entries.  The table contains
                      zero, one, or many rows at any moment, depending upon
                      the number of alarm conditions in effect.  The table
                      is initially empty at agent startup.  The agent
                      creates a row in the table each time a condition is
                      detected and deletes that row when that condition no
                      longer pertains.  The agent creates the first row with
                      upsAlarmId equal to 1, and increments the value of
                      upsAlarmId each time a new row is created, wrapping to
                      the first free value greater than or equal to 1 when
                      the maximum value of upsAlarmId would otherwise be
                      exceeded.  Consequently, after multiple operations,
                      the table may become sparse, e.g., containing entries
                      for rows 95, 100, 101, and 203 and the entries are in
                      chronological order until upsAlarmId wraps.

                      Alarms are named by an OBJECT IDENTIFIER,
                      upsAlarmDescr, to allow a single table to reflect well
                      known alarms plus alarms defined by a particular
                      implementation, i.e., as documented in the private
                      enterprise MIB definition for the device.  No two rows
                      will have the same value of upsAlarmDescr, since
                      alarms define conditions.  In order to meet this
                      requirement, care should be taken in the definition of
                      alarm conditions to insure that a system cannot enter
                      the same condition multiple times simultaneously.





          Expires June 1994                                        [Page 18]





          draft                        UPS MIB                 December 1993


                      The number of active rows in the table at any given
                      time is reflected by the value of upsAlarmsPresent."
              ::= { upsAlarm 2 }

          upsAlarmEntry OBJECT-TYPE
              SYNTAX     UpsAlarmEntry
              MAX-ACCESS not-accessible
              STATUS     current
              DESCRIPTION
                      "An entry containing information applicable to a
                      particular alarm."
              INDEX { upsAlarmId }
              ::= { upsAlarmTable 1 }

          UpsAlarmEntry ::= SEQUENCE {
              upsAlarmId          PositiveInteger,
              upsAlarmDescr       OBJECT IDENTIFIER,
              upsAlarmTime        TimeStamp
          }

          upsAlarmId OBJECT-TYPE
              SYNTAX     PositiveInteger
              MAX-ACCESS not-accessible
              STATUS     current
              DESCRIPTION
                      "A unique identifier for an alarm condition.  This
                      value must remain constant."
              ::= { upsAlarmEntry 1 }

          upsAlarmDescr OBJECT-TYPE
              SYNTAX     OBJECT IDENTIFIER
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "A reference to an alarm description object.  The
                      object referenced should not be accessible, but rather
                      be used to provide a unique description of the alarm
                      condition."
              ::= { upsAlarmEntry 2 }

          upsAlarmTime OBJECT-TYPE
              SYNTAX     TimeStamp
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION





          Expires June 1994                                        [Page 19]





          draft                        UPS MIB                 December 1993


                      "The value of sysUpTime when the alarm condition was
                      detected.  If the alarm condition was detected at the
                      time of agent startup and presumably existed before
                      agent startup, the value of upsAlarmTime shall equal
                      0."
              ::= { upsAlarmEntry 3 }


          --
          -- Well known alarm conditions.
          --

          upsWellKnownAlarms    OBJECT IDENTIFIER ::= { upsAlarm 3 }


          upsAlarmBatteryBad OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "One or more batteries have been determined to require
                      replacement."
              ::= { upsWellKnownAlarms  1 }

          upsAlarmOnBattery OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "The UPS is drawing power from the batteries."
              ::= { upsWellKnownAlarms  2 }

          upsAlarmLowBattery OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "The remaining battery run-time is less than or equal
                      to upsConfigLowBattTime."                               |
              ::= { upsWellKnownAlarms  3 }


          upsAlarmDepletedBattery OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "The UPS will be unable to sustain the present load
                      when and if the utility power is lost."
              ::= { upsWellKnownAlarms  4 }

          upsAlarmTempBad OBJECT-IDENTITY
              STATUS     current





          Expires June 1994                                        [Page 20]





          draft                        UPS MIB                 December 1993


              DESCRIPTION
                      "A temperature is out of tolerance."
              ::= { upsWellKnownAlarms  5 }

          upsAlarmInputBad OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "An input condition is out of tolerance."
              ::= { upsWellKnownAlarms  6 }

          upsAlarmOutputBad OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "An output condition (other than OutputOverload) is
                      out of tolerance."
              ::= { upsWellKnownAlarms  7 }

          upsAlarmOutputOverload OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "The output load exceeds the UPS output capacity."
              ::= { upsWellKnownAlarms  8 }

          upsAlarmOnBypass OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "The Bypass is presently engaged on the UPS."
              ::= { upsWellKnownAlarms  9 }

          upsAlarmBypassBad OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "The Bypass is out of tolerance."
              ::= { upsWellKnownAlarms 10 }

          upsAlarmOutputOffAsRequested OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "The UPS has shutdown as requested, i.e., the output
                      is off."
              ::= { upsWellKnownAlarms 11 }

          upsAlarmUpsOffAsRequested OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION





          Expires June 1994                                        [Page 21]





          draft                        UPS MIB                 December 1993


                      "The entire UPS has shutdown as commanded."
              ::= { upsWellKnownAlarms 12 }

          upsAlarmChargerFailed OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "An uncorrected problem has been detected within the
                      UPS charger subsystem."
              ::= { upsWellKnownAlarms 13 }

          upsAlarmUpsOutputOff OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "The output of the UPS is in the off state."
              ::= { upsWellKnownAlarms 14 }

          upsAlarmUpsSystemOff OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "The UPS system is in the off state."
              ::= { upsWellKnownAlarms 15 }

          upsAlarmFanFailure OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "The failure of one or more fans in the UPS has been
                      detected."
              ::= { upsWellKnownAlarms 16 }

          upsAlarmFuseFailure OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "The failure of one or more fuses has been detected."
              ::= { upsWellKnownAlarms 17 }

          upsAlarmGeneralFault OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "A general fault in the UPS has been detected."
              ::= { upsWellKnownAlarms 18 }

          upsAlarmDiagnosticTestFailed OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "The result of the last diagnostic test indicates a





          Expires June 1994                                        [Page 22]





          draft                        UPS MIB                 December 1993


                      failure."
              ::= { upsWellKnownAlarms 19 }

          upsAlarmCommunicationsLost OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "A problem has been encountered in the communications
                      between the agent and the UPS."
              ::= { upsWellKnownAlarms 20 }

          upsAlarmAwaitingPower OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "The UPS output is off and the UPS is awaiting the
                      return of input power."
              ::= { upsWellKnownAlarms 21 }

          upsAlarmShutdownPending OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "A upsShutdownAfterDelay countdown is underway."
              ::= { upsWellKnownAlarms 22 }

          upsAlarmShutdownImminent OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "The UPS will turn off power to the load in less than
                      5 seconds; this may be either a timed shutdown or a
                      low battery shutdown."
              ::= { upsWellKnownAlarms 23 }

          upsAlarmTestInProgress OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "A test is in progress, as initiated and indicated by
                      the Test Group.  Tests initiated via other
                      implementation-specific mechanisms can indicate the
                      presence of the testing in the alarm table, if
                      desired, via a OBJECT-IDENTITY macro in the MIB
                      document specific to that implementation and are
                      outside the scope of this OBJECT-IDENTITY."
              ::= { upsWellKnownAlarms 24 }








          Expires June 1994                                        [Page 23]





          draft                        UPS MIB                 December 1993


          --
          -- The Test Group
          --

          upsTest               OBJECT IDENTIFIER ::= { upsObjects 7 }

          upsTestId OBJECT-TYPE
              SYNTAX     OBJECT IDENTIFIER
              MAX-ACCESS read-write
              STATUS     current
              DESCRIPTION
                      "The test is named by an OBJECT IDENTIFIER which
                      allows a standard mechanism for the initiation of
                      tests, including the well known tests identified in
                      this document as well as those introduced by a
                      particular implementation, i.e., as documented in the
                      private enterprise MIB definition for the device.

                      Setting this variable initiates the named test. Sets
                      to this variable require the presence of
                      upsTestSpinLock in the same SNMP message.

                      The set request will be rejected with an appropriate
                      error message if the requested test cannot be
                      performed, including attempts to start a test when
                      another test is already in progress.  Tests in
                      progress may be aborted by setting this variable to
                      upsTestAbortTestInProgress.

                      Read operations return the value of the name of the
                      test in progress if a test is in progress or the name
                      of the last test performed if no test is in progress,
                      unless no test has been run, in which case the well
                      known value upsTestNoTestsInitiated is returned."
              ::= { upsTest 1 }

          -- see [10] for more information on the semantics of objects with
          -- syntax of TestAndIncr                                            |

          upsTestSpinLock OBJECT-TYPE
              SYNTAX     TestAndIncr                                          |
              MAX-ACCESS read-write
              STATUS     current
              DESCRIPTION
                      "A spin lock on the test subsystem.  The spinlock is





          Expires June 1994                                        [Page 24]





          draft                        UPS MIB                 December 1993


                      used as follows.

                      Before starting a test, a manager-station should make
                      sure that a test is not in progress as follows:

                          try_again:
                            get (upsTestSpinLock)                             |
                            while (upsTestResultsSummary == inProgress) {     |
                              /* loop while a test is running for another
                      manager */
                              short delay
                              get (upsTestSpinLock)
                            }
                            lock_value = upsTestSpinLock
                            /* no test in progress, start the test */
                            set (upsTestSpinLock = lock_value, upsTestId =
                      requested_test)
                            if (error_index == 1) { /* (upsTestSpinLock
                      failed) */
                              /* if problem is not access control, then
                                  some other manager slipped in ahead of us
                      */
                              goto try_again
                            }
                            if (error_index == 2) { /* (upsTestId) */
                              /* cannot perform the test */
                              give up
                            }
                            /* test started ok */
                            /* wait for test completion by polling
                      upsTestResultsSummary */
                            get (upsTestSpinLock, upsTestResultsSummary,
                      upsTestResultsDetail)
                            while (upsTestResultsSummary == inProgress) {
                              short delay
                              get (upsTestSpinLock, upsTestResultsSummary,
                      upsTestResultsDetail)
                            }
                            /* when test completes, retrieve any additional
                      test results */
                            /* if upsTestSpinLock == lock_value + 1, then
                      these are our test */
                            /* results (as opposed to another manager's */

                            The initial value of upsTestSpinLock at agent





          Expires June 1994                                        [Page 25]





          draft                        UPS MIB                 December 1993


                      initialization shall
                            be 1."
              ::= { upsTest 2 }

          upsTestResultsSummary OBJECT-TYPE
              SYNTAX     INTEGER {
                  donePass(1),
                  doneWarning(2),
                  doneError(3),
                  aborted(4),
                  inProgress(5),
                  noTestsInitiated(6)
              }
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The results of the current or last UPS diagnostics
                      test performed.  The values for donePass(1),
                      doneWarning(2), and doneError(3) are self-documenting.
                      The value aborted(4) is returned for tests which are
                      aborted by setting the value of upsTestId to
                      upsTestAbortTestInProgress.  Tests which have not yet
                      concluded are indicated by inProgress(5).  The value
                      noTestsInitiated(6) indicates that no previous test
                      results are available, such as is the case when no
                      tests have been run since the last reinitialization of
                      the network management subsystem and the system has no
                      provision for non-volatile storage of test results."
              ::= { upsTest 3 }

          upsTestResultsDetail OBJECT-TYPE
              SYNTAX     DisplayString (SIZE (0..255))
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "Additional information about upsTestResultsSummary.
                      If no additional information available, a zero length
                      string is returned."
              ::= { upsTest 4 }

          upsTestStartTime OBJECT-TYPE
              SYNTAX     TimeStamp
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION





          Expires June 1994                                        [Page 26]





          draft                        UPS MIB                 December 1993


                      "The value of sysUpTime at the time the test in
                      progress was initiated, or, if no test is in progress,
                      the time the previous test was initiated.  If the
                      value of upsTestResultsSummary is noTestsInitiated(6),
                      upsTestStartTime has the value 0."
              ::= { upsTest 5 }

          upsTestElapsedTime OBJECT-TYPE
              SYNTAX     TimeInterval
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The amount of time, in TimeTicks, since the test in
                      progress was initiated, or, if no test is in progress,
                      the previous test took to complete.  If the value of
                      upsTestResultsSummary is noTestsInitiated(6),
                      upsTestElapsedTime has the value 0."
              ::= { upsTest 6 }

          --
          -- Well known tests.
          --

          upsWellKnownTests     OBJECT IDENTIFIER ::= { upsTest 7 }


          upsTestNoTestsInitiated OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "No tests have been initiated and no test is in
                      progress."
              ::= { upsWellKnownTests  1 }

          upsTestAbortTestInProgress OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "The test in progress is to be aborted / the test in
                      progress was aborted."
              ::= { upsWellKnownTests  2 }

          upsTestGeneralSystemsTest OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "The manufacturer's standard test of UPS device
                      systems."





          Expires June 1994                                        [Page 27]





          draft                        UPS MIB                 December 1993


              ::= { upsWellKnownTests  3 }

          upsTestQuickBatteryTest OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "A test that is sufficient to determine if the battery
                      needs replacement."
              ::= { upsWellKnownTests  4 }

          upsTestDeepBatteryCalibration OBJECT-IDENTITY
              STATUS     current
              DESCRIPTION
                      "The system is placed on battery to a discharge level,
                      set by the manufacturer, sufficient to determine
                      battery replacement and battery run-time with a high
                      degree of confidence.  WARNING:  this test will leave
                      the battery in a low charge state and will require
                      time for recharging to a level sufficient to provide
                      normal battery duration for the protected load."
              ::= { upsWellKnownTests  5 }






























          Expires June 1994                                        [Page 28]





          draft                        UPS MIB                 December 1993


          --
          -- The Control group.
          --

          upsControl            OBJECT IDENTIFIER ::= { upsObjects 8 }

          upsShutdownType OBJECT-TYPE
              SYNTAX     INTEGER {
                  output(1),
                  system(2)
              }
              MAX-ACCESS read-write
              STATUS     current
              DESCRIPTION
                      "This object determines the action taken by the
                      upsShutdownAfterDelay and upsRebootWithDuration
                      objects.  Setting this object to output(1) indicates
                      that shutdown requests should cause only the output of
                      the UPS to turn off.  Setting this object to system(2)
                      indicates that shutdown requests will cause the entire
                      UPS system to turn off."
              ::= { upsControl 1 }

          upsShutdownAfterDelay OBJECT-TYPE
              SYNTAX     INTEGER (-1..2147483648)
              UNITS      "seconds"
              MAX-ACCESS read-write
              STATUS     current
              DESCRIPTION
                      "Setting this object will shutdown (i.e., turn off)
                      either the UPS output or the UPS system (as determined
                      by the value of upsShutdownType at the time of
                      shutdown) after the indicated number of seconds, or
                      less if the UPS batteries become depleted. Setting
                      this object to 0 will cause the shutdown to occur
                      immediately.  Setting this object to -1 will abort the
                      countdown.  If the system is already in the desired
                      state at the time the countdown reaches 0, then
                      nothing will happen.  That is, there is no additional
                      action at that time if upsShutdownType = system and
                      the system is already off.  Similarly, there is no
                      additional action at that time if upsShutdownType =
                      output and the output is already off.  When read,
                      upsShutdownAfterDelay will return the number of
                      seconds remaining until shutdown, or -1 if no shutdown





          Expires June 1994                                        [Page 29]





          draft                        UPS MIB                 December 1993


                      countdown is in effect.  On some systems, if the agent
                      is restarted while a shutdown countdown is in effect,
                      the countdown may be aborted.  Sets to this object
                      override any upsShutdownAfterDelay already in effect."
              ::= { upsControl 2 }

          upsStartupAfterDelay OBJECT-TYPE
              SYNTAX     INTEGER (-1..2147483648)
              UNITS      "seconds"
              MAX-ACCESS read-write
              STATUS     current
              DESCRIPTION
                      "Setting this object will start the output after the
                      indicated number of seconds, including starting the
                      UPS, if necessary.  Setting this object to 0 will
                      cause the startup to occur immediately.  Setting this
                      object to -1 will abort the countdown.  If the output
                      is already on at the time the countdown reaches 0,
                      then nothing will happen.  Sets to this object
                      override the effect of any upsStartupAfterDelay
                      countdown or upsRebootWithDuration countdown in
                      progress.  When read, upsStartupAfterDelay will return
                      the number of seconds until startup, or -1 if no
                      startup countdown is in effect.  If the countdown
                      expires during a utility failure, the startup shall
                      depend upon the value of upsAutoRestart at that time.
                      On some systems, if the agent is restarted while a
                      startup countdown is in effect, the countdown is
                      aborted."
              ::= { upsControl 3 }                                            |

          upsRebootWithDuration OBJECT-TYPE
              SYNTAX     INTEGER (-1..300)
              UNITS      "seconds"
              MAX-ACCESS read-write
              STATUS     current
              DESCRIPTION
                      "Setting this object will immediately shutdown (i.e.,
                      turn off) either the UPS output or the UPS system (as
                      determined by the value of upsShutdownType at the time
                      of shutdown) for a period equal to the indicated
                      number of seconds, after which time the output will be
                      started, including starting the UPS, if necessary.  If
                      the number of seconds required to perform the request
                      is greater than the requested duration, then the





          Expires June 1994                                        [Page 30]





          draft                        UPS MIB                 December 1993


                      requested shutdown and startup cycle shall be
                      performed in the minimum time possible, but in no case
                      shall this require more than the requested duration
                      plus 60 seconds.  When read, upsRebootWithDuration
                      shall return the number of seconds remaining in the
                      countdown, or -1 if no countdown is in progress.  If
                      the startup should occur during a utility failure, the
                      startup shall depend upon the value of upsAutoRestart
                      at that time."
              ::= { upsControl 4 }                                            |

          upsAutoRestart OBJECT-TYPE
              SYNTAX     INTEGER {
                  on(1),
                  off(2)
              }
              MAX-ACCESS read-write
              STATUS     current
              DESCRIPTION
                      "Setting this object to 'on' will cause the UPS system
                      to restart after a shutdown if/when utility power is    |
                      present.  Setting this object to 'off' will prevent     |
                      the UPS system from restarting after a shutdown until   |
                      an operator manually or remotely explicitly restarts    |
                      it."                                                    |
              ::= { upsControl 5 }                                            |
























          Expires June 1994                                        [Page 31]





          draft                        UPS MIB                 December 1993


          --
          -- The Configuration group.
          --

          upsConfig             OBJECT IDENTIFIER ::= { upsObjects 9 }

          upsConfigInputVoltage OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "RMS Volts"
              MAX-ACCESS read-write
              STATUS     current
              DESCRIPTION
                      "The magnitude of the nominal input voltage.  On those
                      systems which support read-write access to this
                      object, if there is an attempt to set this variable to
                      a value that is not supported, the request must be
                      rejected and the agent shall respond with an
                      appropriate error message, i.e., badValue for SNMPv1,
                      or inconsistentValue for SNMPv2."
              ::= { upsConfig 1 }

          upsConfigInputFreq OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "0.1 Hertz"
              MAX-ACCESS read-write
              STATUS     current
              DESCRIPTION
                      "The nominal input frequency.  On those systems which
                      support read-write access to this object, if there is
                      an attempt to set this variable to a value that is not
                      supported, the request must be rejected and the agent
                      shall respond with an appropriate error message, i.e.,
                      badValue for SNMPv1, or inconsistentValue for SNMPv2."
              ::= { upsConfig 2 }

          upsConfigOutputVoltage OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "RMS Volts"
              MAX-ACCESS read-write
              STATUS     current
              DESCRIPTION
                      "The magnitude of the nominal output voltage.  On
                      those systems which support read-write access to this
                      object, if there is an attempt to set this variable to
                      a value that is not supported, the request must be





          Expires June 1994                                        [Page 32]





          draft                        UPS MIB                 December 1993


                      rejected and the agent shall respond with an
                      appropriate error message, i.e., badValue for SNMPv1,
                      or inconsistentValue for SNMPv2."
              ::= { upsConfig 3 }

          upsConfigOutputFreq OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "0.1 Hertz"
              MAX-ACCESS read-write
              STATUS     current
              DESCRIPTION
                      "The nominal output frequency.  On those systems which
                      support read-write access to this object, if there is
                      an attempt to set this variable to a value that is not
                      supported, the request must be rejected and the agent
                      shall respond with an appropriate error message, i.e.,
                      badValue for SNMPv1, or inconsistentValue for SNMPv2."
              ::= { upsConfig 4 }

          upsConfigOutputVA OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "Volt-Amps"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The magnitude of the nominal Volt-Amp rating."
              ::= { upsConfig 5 }

          upsConfigOutputPower OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "Watts"
              MAX-ACCESS read-only
              STATUS     current
              DESCRIPTION
                      "The magnitude of the nominal true power rating."
              ::= { upsConfig 6 }

          upsConfigLowBattTime OBJECT-TYPE                                    |
              SYNTAX     NonNegativeInteger
              UNITS      "minutes"
              MAX-ACCESS read-write
              STATUS     current
              DESCRIPTION
                      "The value of upsEstimatedMinutesRemaining at which a
                      lowBattery condition is declared.  For agents which





          Expires June 1994                                        [Page 33]





          draft                        UPS MIB                 December 1993


                      support only discrete (discontinuous) values, then the
                      agent shall round up to the next supported value.  If
                      the requested value is larger than the largest
                      supported value, then the largest supported value
                      shall be selected."
              ::= { upsConfig 7 }

          upsConfigAudibleStatus OBJECT-TYPE
              SYNTAX     INTEGER {
                  disabled(1),
                  enabled(2),
                  muted(3)
              }
              MAX-ACCESS read-write
              STATUS     current
              DESCRIPTION
                      "The requested state of the audible alarm.  When in
                      the disabled state, the audible alarm should never
                      sound.  The enabled state is self-describing.  Setting
                      this object to muted(3) when the audible alarm is
                      sounding shall temporarily silence the alarm.  It will
                      remain muted until it would normally stop sounding and
                      the value returned for read operations during this
                      period shall equal muted(3).  At the end of this
                      period, the value shall revert to enabled(2).  Writes
                      of the value muted(3) when the audible alarm is not
                      sounding shall be accepted but shall have no effect."
              ::= { upsConfig 8 }

          upsConfigLowVoltageTransferPoint OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "RMS Volts"
              MAX-ACCESS read-write
              STATUS     current
              DESCRIPTION
                      "The minimum input line voltage allowed before the UPS
                      system transfers to battery backup."
              ::= { upsConfig 9 }

          upsConfigHighVoltageTransferPoint OBJECT-TYPE
              SYNTAX     NonNegativeInteger
              UNITS      "RMS Volts"
              MAX-ACCESS read-write
              STATUS     current
              DESCRIPTION





          Expires June 1994                                        [Page 34]





          draft                        UPS MIB                 December 1993


                      "The maximum line voltage allowed before the UPS
                      system transfers to battery backup."
              ::= { upsConfig 10 }















































          Expires June 1994                                        [Page 35]





          draft                        UPS MIB                 December 1993


          --
          -- notifications, i.e., traps
          --
          upsTraps              OBJECT IDENTIFIER ::= { upsMibE26 2 }         |

          -- This section defines the well-known notifications sent by        |
          -- UPS agents.                                                      |
          -- Care must be taken to insure that no particular notification
          -- is sent to a single receiving entity more often than once
          -- every five seconds.

          upsTrapOnBattery NOTIFICATION-TYPE
              OBJECTS { upsEstimatedMinutesRemaining, upsSecondsOnBattery,
                        upsConfigLowBattTime }                                |
              STATUS  current
              DESCRIPTION
                      "The UPS is operating on battery power.  This trap is
                      persistent and is resent at one minute intervals until
                      the UPS either turns off or is no longer running on
                      battery."
            ::= { upsTraps 1 }

          upsTrapTestCompleted NOTIFICATION-TYPE
              OBJECTS { upsTestId, upsTestSpinLock,
                        upsTestResultsSummary, upsTestResultsDetail,
                        upsTestStartTime, upsTestElapsedTime }
              STATUS  current
              DESCRIPTION
                      "This trap is sent upon completion of a UPS diagnostic
                      test."
            ::= { upsTraps 2 }

          upsTrapAlarmEntryAdded NOTIFICATION-TYPE
              OBJECTS { upsAlarmId, upsAlarmDescr }
              STATUS  current
              DESCRIPTION
                      "This trap is sent each time an alarm is inserted into
                      to the alarm table.  It is sent on the insertion all
                      alarms except for upsAlarmOnBattery and
                      upsAlarmTestInProgress."
            ::= { upsTraps 3 }

          upsTrapAlarmEntryRemoved NOTIFICATION-TYPE
              OBJECTS { upsAlarmId, upsAlarmDescr }
              STATUS  current





          Expires June 1994                                        [Page 36]





          draft                        UPS MIB                 December 1993


              DESCRIPTION
                      "This trap is sent each time an alarm is removed from
                      the alarm table.  It is sent on the removal of all      |
                      alarms except for upsAlarmTestInProgress."              |
            ::= { upsTraps 4 }













































          Expires June 1994                                        [Page 37]





          draft                        UPS MIB                 December 1993


          --
          -- conformance information
          --
          upsConformance        OBJECT IDENTIFIER ::= { upsMibE26 3 }         |

          upsCompliances        OBJECT IDENTIFIER ::= { upsConformance 1 }


          --
          -- compliance statements
          --

          upsSubsetCompliance MODULE-COMPLIANCE
              STATUS     current
              DESCRIPTION

                      "The compliance statement for UPSs that only support
                      the basic two-contact communication protocol."
               MODULE -- this module
                   MANDATORY-GROUPS  { upsSubsetIdentGroup, upsSubsetBatteryGroup,
                            upsSubsetInputGroup, upsSubsetOutputGroup,
                            upsSubsetAlarmGroup,
                            upsSubsetControlGroup, upsSubsetConfigGroup }

              OBJECT     upsBatteryStatus
              SYNTAX     INTEGER {
                  batteryNormal(2),
                  batteryLow(3)
              }
              DESCRIPTION
                      "Support of the values unknown(1) and
                      batteryDepleted(4) is not required."

              OBJECT     upsAlarmDescr
              DESCRIPTION
                      "Support of all `well known' alarm types is not
                      required.  The well known alarm types which must be
                      supported are:                                          -
                      upsAlarmOnBattery, upsAlarmLowBattery,                  -
                      upsAlarmInputBad,                                       -
                      upsAlarmUpsOutputOff, upsAlarmUpsSystemOff,             -
                      and upsAlarmTestInProgress."

              OBJECT     upsOutputSource
              SYNTAX     INTEGER {





          Expires June 1994                                        [Page 38]





          draft                        UPS MIB                 December 1993


                  normal(2),
                  battery(4)
              }
              DESCRIPTION
                      "Support of the values other(1), none(2), bypass(4),    |
                      booster(6) and reducer(7)                               |
                      is not required."

              OBJECT     upsShutdownType
              MIN-ACCESS read-only
              DESCRIPTION
                      "Read-write access is not required, i.e., compliant
                      systems need not support more than one shutdown type."

              OBJECT     upsAutoRestart                                       +
              MIN-ACCESS read-only                                            +
              DESCRIPTION                                                     +
                      "Read-write access is not required, i.e., compliant     +
                      systems need not support more than one restart type."   +

              OBJECT     upsConfigInputVoltage
              MIN-ACCESS read-only
              DESCRIPTION
                      "Read-write access is not required."

              OBJECT     upsConfigInputFreq
              MIN-ACCESS read-only
              DESCRIPTION
                      "Read-write access is not required."

              OBJECT     upsConfigOutputVoltage
              MIN-ACCESS read-only
              DESCRIPTION
                      "Read-write access is not required."

              OBJECT     upsConfigOutputFreq
              MIN-ACCESS read-only
              DESCRIPTION
                      "Read-write access is not required."

              ::= { upsCompliances 1 }

          upsBasicCompliance MODULE-COMPLIANCE
              STATUS     current
              DESCRIPTION





          Expires June 1994                                        [Page 39]





          draft                        UPS MIB                 December 1993


                      "The compliance statement for UPSs that support
                      full-featured functions, such as control."
              MODULE -- this module
                  MANDATORY-GROUPS { upsBasicIdentGroup, upsBasicBatteryGroup,
                            upsBasicInputGroup, upsBasicOutputGroup,
                            upsBasicAlarmGroup, upsBasicTestGroup,
                            upsBasicControlGroup, upsBasicConfigGroup }


              OBJECT     upsAlarmDescr
              DESCRIPTION
                      "Support of all `well known' alarm types is not
                      required.  The well known alarm types which must be
                      supported are: upsAlarmOnBattery, upsAlarmLowBattery,   +
                      upsAlarmDepletedBattery, upsAlarmTempBad,               +
                      upsAlarmInputBad, upsAlarmOutputOverload,               +
                      upsAlarmOnBypass, upsAlarmBypassBad,                    +
                      upsAlarmOutputOffAsRequested,                           +
                      upsAlarmUpsOffAsRequested,                              +
                      upsAlarmUpsOutputOff, upsAlarmUpsSystemOff,             +
                      upsAlarmGeneralFault, upsAlarmDiagnosticTestFailed,     +
                      upsAlarmCommunicationsLost, upsAlarmShutdownPending,    +
                      and upsAlarmTestInProgress."

              OBJECT     upsTestId
              DESCRIPTION
                      "Support of all `well known' test types is not
                      required.  If no tests are supported, then the testing
                      The well known test types which must be supported are:  |
                      upsTestNoTestsInitiated."                               |

              OBJECT     upsOutputSource
              SYNTAX     INTEGER {
                  normal(2),
                  battery(4)
              }
              DESCRIPTION
                      "Support of the values other(1), none(2), bypass(4),    |
                      booster(6) and reducer(7)                               |
                      is not required."

                  GROUP upsBasicBypassGroup
                  DESCRIPTION
                      "The upsBasicBypassGroup is only required for UPSs
                      that have a Bypass present."





          Expires June 1994                                        [Page 40]





          draft                        UPS MIB                 December 1993


              OBJECT     upsShutdownType
              MIN-ACCESS read-only
              DESCRIPTION
                      "Read-write access is not required, i.e., compliant
                      systems need not support more than one shutdown type."

              OBJECT     upsAutoRestart                                       +
              MIN-ACCESS read-only                                            +
              DESCRIPTION                                                     +
                      "Read-write access is not required, i.e., compliant     +
                      systems need not support more than one restart type."   +

              OBJECT     upsConfigInputVoltage
              MIN-ACCESS read-only
              DESCRIPTION
                      "Read-write access is not required."

              OBJECT     upsConfigInputFreq
              MIN-ACCESS read-only
              DESCRIPTION
                      "Read-write access is not required."

              OBJECT     upsConfigOutputVoltage
              MIN-ACCESS read-only
              DESCRIPTION
                      "Read-write access is not required."

              OBJECT     upsConfigOutputFreq
              MIN-ACCESS read-only
              DESCRIPTION
                      "Read-write access is not required."

              OBJECT     upsConfigLowBattTime                                 |
              DESCRIPTION
                      "Implementation of all possible values may be onerous
                      for some systems.  Consequently, not all possible
                      values must be supported.  However, at least two
                      different manufactuerer-selected values must be
                      supported."

              ::= { upsCompliances 2 }

          upsFullCompliance MODULE-COMPLIANCE
              STATUS     current
              DESCRIPTION





          Expires June 1994                                        [Page 41]





          draft                        UPS MIB                 December 1993


                      "The compliance statement for UPSs that support
                      advanced full-featured functions."
              MODULE -- this module
                  MANDATORY-GROUPS { upsFullIdentGroup, upsFullBatteryGroup,
                            upsFullInputGroup, upsFullOutputGroup,
                            upsFullAlarmGroup, upsFullTestGroup,
                            upsFullControlGroup, upsFullConfigGroup }

              OBJECT     upsAlarmDescr
              DESCRIPTION
                      "Support of all `well known' alarm types is not
                      required.  The well known alarm types which must be
                      supported are: upsAlarmBatteryBad, upsAlarmOnBattery,
                      upsAlarmLowBattery, upsAlarmDepletedBattery,
                      upsAlarmTempBad, upsAlarmInputBad, upsAlarmOnBypass,
                      upsAlarmBypassBad, upsAlarmOutputOffAsRequested,
                      upsAlarmUpsOffAsRequested, upsAlarmUpsOutputOff,
                      upsAlarmUpsSystemOff, upsAlarmGeneralFault,
                      upsAlarmDiagnosticTestFailed,
                      upsAlarmCommunicationsLost,                             -
                      upsAlarmShutdownPending, and upsAlarmTestInProgress."

              OBJECT     upsTestId
              DESCRIPTION
                      "Support of all `well known' test types is not
                      required.  The well known test types which must be
                      supported are: upsTestNoTestsInitiated,
                      upsTestGeneralSystemsTest,                              -
                      and upsTestQuickBatteryTest."                           |

              OBJECT     upsOutputSource
              SYNTAX     INTEGER {
                  normal(2),
                  battery(4)
              }
              DESCRIPTION
                      "Support of the values other(1), none(2), bypass(4),    |
                      booster(6) and reducer(7)                               |
                      is not required."

                  GROUP upsFullBypassGroup
                  DESCRIPTION
                      "The upsFullBypassGroup is only required for UPSs that
                      have a Bypass present."






          Expires June 1994                                        [Page 42]





          draft                        UPS MIB                 December 1993


              OBJECT     upsShutdownType
              MIN-ACCESS read-only
              DESCRIPTION
                      "Read-write access is not required, i.e., compliant
                      systems need not support more than one shutdown type."

              OBJECT     upsAutoRestart                                       +
              MIN-ACCESS read-only                                            +
              DESCRIPTION                                                     +
                      "Read-write access is not required, i.e., compliant     +
                      systems need not support more than one restart type."   +

              OBJECT     upsConfigInputVoltage
              MIN-ACCESS read-only
              DESCRIPTION
                      "Read-write access is not required."

              OBJECT     upsConfigInputFreq
              MIN-ACCESS read-only
              DESCRIPTION
                      "Read-write access is not required."

              OBJECT     upsConfigOutputVoltage
              MIN-ACCESS read-only
              DESCRIPTION
                      "Read-write access is not required."

              OBJECT     upsConfigOutputFreq
              MIN-ACCESS read-only
              DESCRIPTION
                      "Read-write access is not required."

              OBJECT     upsConfigLowBattTime                                 |
              DESCRIPTION
                      "Implementation of all possible values may be onerous
                      for some systems.  Consequently, not all possible
                      values must be supported.  However, at least two
                      different manufactuerer-selected values must be
                      supported."

              ::= { upsCompliances 3 }









          Expires June 1994                                        [Page 43]





          draft                        UPS MIB                 December 1993


          --
          -- units of conformance
          --

          -- summary at a glance:

          --                                      subset  basic   adv
          --upsIdentManufacturer                  x       x       x
          --upsIdentModel                         x       x       x
          --upsIdentUPSSoftwareVersion                    x       x           |
          --upsIdentAgentSoftwareVersion          x       x       x
          --upsIdentName                          x       x       x
          --upsIdentAttachedDevices               x               x
          --
          --upsBatteryStatus                      x       x       x       notes
          --upsSecondsOnBattery                   x       x       x
          --upsEstimatedMinutesRemaining                          x           |
          --upsEstimatedChargeRemaining                           x           |
          --upsBatteryVoltage
          --upsBatteryCurrent
          --upsBatteryTemperature
          --
          --upsInputFrequency                             x       x
          --upsInputLineBads                      x       x       x
          --upsInputNumLines                              x       x
          --upsInputVoltage                               x       x
          --upsInputCurrent
          --upsInputTruePower                                                 |
          --
          --upsOutputSource                       x       x       x       notes
          --upsOutputFrequency                            x       x
          --upsOutputNumLines                             x       x
          --upsOutputVoltage                              x       x
          --upsOutputCurrent                                      x
          --upsOutputPower                                        x
          --upsOutputPercentLoad                                  x
          --
          --
          --upsBypassFrequency                            x       x       iff note
          --upsBypassNumLines                             x       x
          --upsBypassVoltage                              x       x
          --upsBypassCurrent
          --upsBypassPower
          --
          --





          Expires June 1994                                        [Page 44]





          draft                        UPS MIB                 December 1993


          --upsAlarmsPresent                      x       x       x
          --upsAlarmDescr                         x       x       x       notes
          --upsAlarmTime                          x       x       x
          --
          --upsTestId                                     x       x       notes
          --upsTestSpinLock                               x       x
          --upsTestResultsSummary                         x       x
          --upsTestResultsDetail                          x       x
          --upsTestStartTime                              x       x
          --upsTestElapsedTime                            x       x
          --
          --upsShutdownType                       x       x       x       notes
          --upsShutdownAfterDelay                 x       x       x
          --upsStartupAfterDelay                          x       x
          --upsRebootWithDuration                         x       x
          --upsAutoRestart                        x       x       x       notes|
          --
          --upsConfigInputVoltage                 x       x       x       notes
          --upsConfigInputFreq                    x       x       x       notes
          --upsConfigOutputVoltage                x       x       x       notes
          --upsConfigOutputFreq                   x       x       x       notes
          --upsConfigOutputVA                     x       x       x
          --upsConfigOutputPower                  x       x       x
          --upsConfigLowBattTime                          x       x       at least 2|
          --upsConfigAudibleStatus                        x       x
          --upsConfigLowVoltageTransferPoint
          --upsConfigHighVoltageTransferPoint























          Expires June 1994                                        [Page 45]





          draft                        UPS MIB                 December 1993


          -- units of conformance
          upsGroups             OBJECT IDENTIFIER ::= { upsConformance 2 }

          upsSubsetGroups       OBJECT IDENTIFIER ::= { upsGroups 1 }

          upsSubsetIdentGroup OBJECT-GROUP
              OBJECTS { upsIdentManufacturer, upsIdentModel,
                        upsIdentAgentSoftwareVersion, upsIdentName,           -
                        upsIdentAttachedDevices }
              STATUS  current
              DESCRIPTION
                      "The upsSubsetIdentGroup defines objects which are
                      common across all UPSs which meet subset compliance."
              ::= { upsSubsetGroups 1 }

          upsSubsetBatteryGroup OBJECT-GROUP
              OBJECTS { upsBatteryStatus, upsSecondsOnBattery }
              STATUS  current
              DESCRIPTION
                      "The upsSubsetBatteryGroup defines the objects that
                      are common to battery groups of two-contact UPSs."
              ::= { upsSubsetGroups 2 }

          upsSubsetInputGroup OBJECT-GROUP
              OBJECTS { upsInputLineBads }
              STATUS  current
              DESCRIPTION
                      "The upsSubsetInputGroup defines the objects that are
                      common to the Input groups of two-contact UPSs."
              ::= { upsSubsetGroups 3 }

          upsSubsetOutputGroup OBJECT-GROUP
              OBJECTS { upsOutputSource }
              STATUS  current
              DESCRIPTION
                      "The upsSubsetOutputGroup defines the objects that are
                      common to the Output groups of two-contact UPSs."
              ::= { upsSubsetGroups 4 }

          -- { upsSubsetGroups 5 } is reserved for future use (upsSubsetBypassGroup)

          upsSubsetAlarmGroup OBJECT-GROUP
              OBJECTS { upsAlarmsPresent, upsAlarmDescr, upsAlarmTime }
              STATUS  current
              DESCRIPTION





          Expires June 1994                                        [Page 46]





          draft                        UPS MIB                 December 1993


                      "The upsSubsetAlarmGroup defines the objects that are
                      common to the Alarm groups of basic two-contact UPSs."
              ::= { upsSubsetGroups 6 }

          -- { upsSubsetGroups 7 } is reserved for future use (upsSubsetTestGroup)

          upsSubsetControlGroup OBJECT-GROUP
              OBJECTS { upsShutdownType, upsShutdownAfterDelay,
                            upsAutoRestart }
              STATUS  current
              DESCRIPTION
                      "The upsSubsetControlGroup defines the objects that
                      are common to the Control groups of basic two-contact
                      UPSs."
              ::= { upsSubsetGroups 8 }

          upsSubsetConfigGroup OBJECT-GROUP
              OBJECTS { upsConfigInputVoltage, upsConfigInputFreq,
                        upsConfigOutputVoltage, upsConfigOutputFreq,
                        upsConfigOutputVA, upsConfigOutputPower }
              STATUS  current
              DESCRIPTION
                      "The upsSubsetConfigGroup defines the objects that are
                      common to the Config groups of basic two-contact
                      UPSs."
              ::= { upsSubsetGroups 9 }

          upsBasicGroups        OBJECT IDENTIFIER ::= { upsGroups 2 }

          upsBasicIdentGroup OBJECT-GROUP
              OBJECTS { upsIdentManufacturer, upsIdentModel,
                        upsIdentUPSSoftwareVersion,
                        upsIdentAgentSoftwareVersion, upsIdentName }
              STATUS  current
              DESCRIPTION
                      "The upsBasicIdentGroup defines objects which are
                      common to the Ident group of compliant UPSs which
                      support basic functions."
              ::= { upsBasicGroups 1 }

          upsBasicBatteryGroup OBJECT-GROUP
              OBJECTS { upsBatteryStatus, upsSecondsOnBattery }               |
              STATUS  current
              DESCRIPTION
                      "The upsBasicBatteryGroup defines the objects that are





          Expires June 1994                                        [Page 47]





          draft                        UPS MIB                 December 1993


                      common to the battery groups of compliant UPSs which
                      support basic functions."
              ::= { upsBasicGroups 2 }

          upsBasicInputGroup OBJECT-GROUP
              OBJECTS { upsInputFrequency, upsInputLineBads,
                        upsInputNumLines, upsInputVoltage }                   |
              STATUS  current
              DESCRIPTION
                      "The upsBasicInputGroup defines the objects that are
                      common to the Input groups of compliant UPSs which
                      support basic functions."
              ::= { upsBasicGroups 3 }

          upsBasicOutputGroup OBJECT-GROUP
              OBJECTS { upsOutputSource, upsOutputFrequency,
                        upsOutputNumLines, upsOutputVoltage }
              STATUS  current
              DESCRIPTION
                      "The upsBasicOutputGroup defines the objects that are
                      common to the Output groups of compliant UPSs which
                      support basic functions."
              ::= { upsBasicGroups 4 }

          upsBasicBypassGroup OBJECT-GROUP
              OBJECTS { upsBypassFrequency, upsBypassNumLines,
                        upsBypassVoltage }
              STATUS  current
              DESCRIPTION
                      "The upsBasicBypassGroup defines the objects that are
                      common to the Bypass groups of compliant UPSs which
                      support basic functions."
              ::= { upsBasicGroups 5 }

          upsBasicAlarmGroup OBJECT-GROUP
              OBJECTS { upsAlarmsPresent, upsAlarmDescr, upsAlarmTime }
              STATUS  current
              DESCRIPTION

                      "The upsBasicAlarmGroup defines the objects that are
                      common to the Alarm  groups of compliant UPSs which
                      support basic functions."
              ::= { upsBasicGroups 6 }

          upsBasicTestGroup OBJECT-GROUP





          Expires June 1994                                        [Page 48]





          draft                        UPS MIB                 December 1993


              OBJECTS { upsTestId, upsTestSpinLock,
                        upsTestResultsSummary, upsTestResultsDetail,
                        upsTestStartTime, upsTestElapsedTime }
              STATUS  current
              DESCRIPTION
                      "The upsBasicTestGroup defines the objects that are
                      common to the Test groups of compliant UPSs which
                      support basic functions."
              ::= { upsBasicGroups 7 }

          upsBasicControlGroup OBJECT-GROUP
              OBJECTS { upsShutdownType, upsShutdownAfterDelay,
                        upsStartupAfterDelay, upsRebootWithDuration,
                        upsAutoRestart }
              STATUS  current
              DESCRIPTION
          "The upsBasicControlGroup defines the objects that are
          common to the Control groups of compliant UPSs which support basic functions."
              ::= { upsBasicGroups 8 }

          upsBasicConfigGroup OBJECT-GROUP
              OBJECTS { upsConfigInputVoltage, upsConfigInputFreq,
                        upsConfigOutputVoltage, upsConfigOutputFreq,
                        upsConfigOutputVA, upsConfigOutputPower,
                        upsConfigLowBattTime, upsConfigAudibleStatus }        |
              STATUS  current
              DESCRIPTION
                      "The upsBasicConfigGroup defines the objects that are
                      common to the Config groups of UPSs which support
                      basic functions."
              ::= { upsBasicGroups 9 }

          upsFullGroups         OBJECT IDENTIFIER ::= { upsGroups 3 }

          upsFullIdentGroup OBJECT-GROUP
              OBJECTS { upsIdentManufacturer, upsIdentModel,
                        upsIdentUPSSoftwareVersion,
                        upsIdentAgentSoftwareVersion, upsIdentName,
                        upsIdentAttachedDevices }
              STATUS  current
              DESCRIPTION
                      "The upsFullIdentGroup defines objects which are
                      common to the Ident group of fully compliant UPSs."
              ::= { upsFullGroups 1 }






          Expires June 1994                                        [Page 49]





          draft                        UPS MIB                 December 1993


          upsFullBatteryGroup OBJECT-GROUP
              OBJECTS { upsBatteryStatus, upsSecondsOnBattery,
                        upsEstimatedMinutesRemaining, upsEstimatedChargeRemaining }
              STATUS  current
              DESCRIPTION
                      "The upsFullBatteryGroup defines the objects that are
                      common to the battery groups of fully compliant UPSs."
              ::= { upsFullGroups 2 }

          upsFullInputGroup OBJECT-GROUP
              OBJECTS { upsInputFrequency, upsInputLineBads,
                        upsInputNumLines, upsInputVoltage }                   |
              STATUS  current
              DESCRIPTION
                      "The upsFullInputGroup defines the objects that are
                      common to the Input groups of fully compliant UPSs."
              ::= { upsFullGroups 3 }

          upsFullOutputGroup OBJECT-GROUP
              OBJECTS { upsOutputSource, upsOutputFrequency,
                        upsOutputNumLines, upsOutputVoltage,                  |
                        upsOutputCurrent, upsOutputPower,
                        upsOutputPercentLoad }
              STATUS  current
              DESCRIPTION
                      "The upsFullOutputGroup defines the objects that are
                      common to the Output groups of fully compliant UPSs."
              ::= { upsFullGroups 4 }

          upsFullBypassGroup OBJECT-GROUP
              OBJECTS { upsBypassFrequency, upsBypassNumLines,
                        upsBypassVoltage }
              STATUS  current
              DESCRIPTION
                      "The upsFullBypassGroup defines the objects that are
                      common to the Bypass groups of fully compliant UPSs."
              ::= { upsFullGroups 5 }

          upsFullAlarmGroup OBJECT-GROUP
              OBJECTS { upsAlarmsPresent, upsAlarmDescr, upsAlarmTime }
              STATUS  current
              DESCRIPTION

                      "The upsFullAlarmGroup defines the objects that are
                      common to the Alarm  groups of fully compliant UPSs."





          Expires June 1994                                        [Page 50]





          draft                        UPS MIB                 December 1993


              ::= { upsFullGroups 6 }

          upsFullTestGroup OBJECT-GROUP
              OBJECTS { upsTestId, upsTestSpinLock,
                        upsTestResultsSummary, upsTestResultsDetail,
                        upsTestStartTime, upsTestElapsedTime }
              STATUS  current
              DESCRIPTION
                      "The upsFullTestGroup defines the objects that are
                      common to the Test groups of fully compliant UPSs."
              ::= { upsFullGroups 7 }

          upsFullControlGroup OBJECT-GROUP
              OBJECTS { upsShutdownType, upsShutdownAfterDelay,
                        upsStartupAfterDelay, upsRebootWithDuration,
                        upsAutoRestart }
              STATUS  current
              DESCRIPTION
          "The upsFullControlGroup defines the objects that are
          common to the Control groups of fully compliant UPSs."
              ::= { upsFullGroups 8 }

          upsFullConfigGroup OBJECT-GROUP
              OBJECTS { upsConfigInputVoltage, upsConfigInputFreq,
                        upsConfigOutputVoltage, upsConfigOutputFreq,
                        upsConfigOutputVA, upsConfigOutputPower,
                        upsConfigLowBattTime, upsConfigAudibleStatus }        |
              STATUS  current
              DESCRIPTION
                      "The upsFullConfigGroup defines the objects that are
                      common to the Config groups of UPSs."
              ::= { upsFullGroups 9 }

          END
















          Expires June 1994                                        [Page 51]





          draft                        UPS MIB                 December 1993


          6.  Acknowledgements

          The UPS MIB represents the combined work of the IETF UPS MIB
          Working Group, with particular, substantial authorship
          contributions from:

           Mike Davison
           Fibercom, Inc.

           Ray Wasson
           Consultant

           Roger Draper
           Liebert Corporation

           Ken Key
           SNMP Research, Incorporated

           Pete Yoest
           American Power Conversion

           Doug Rademacher
           American Power Conversion

           Ron Pitt
           Network Security Systems, Inc

           Terry Zumwalt
           International Power Machines

           Lawren Markle
           Tripp Lite

           Bill Elliot
           ONEAC

           Tom Brennan
           Exide Electronics

           Brian Young
           Best Power Technology









          Expires June 1994                                        [Page 52]





          draft                        UPS MIB                 December 1993


          7.  References

          [1]  M.T. Rose and K. McCloghrie, Structure and Identification of
               Management Information for TCP/IP-based internets, Internet
               Working Group Request for Comments 1155.  Network Information
               Center, SRI International, Menlo Park, California, (May,
               1990).

          [2]  K. McCloghrie and M.T. Rose, Management Information Base for
               Network Management of TCP/IP-based internets, Internet
               Working Group Request for Comments 1156.  Network Information
               Center, SRI International, Menlo Park, California, (May,
               1990).

          [3]  J.D. Case, M.S. Fedor, M.L. Schoffstall, and J.R. Davin,
               Simple Network Management Protocol, Internet Working Group
               Request for Comments 1157.  Network Information Center, SRI
               International, Menlo Park, California, (May, 1990).

          [4]  K. McCloghrie and M.T. Rose (editors), Management Information
               Base for Network Management of TCP/IP-based internets: MIB-
               II, Internet Working Group Request for Comments 1213.
               Network Information Center, SRI International, Menlo Park,
               California, (March, 1991).

          [5]  Information processing systems - Open Systems Interconnection
               - Specification of Abstract Syntax Notation One (ASN.1),
               International Organization for Standardization.
               International Standard 8824, (December, 1987).

          [6]  Information processing systems - Open Systems Interconnection
               - Specification of Basic Encoding Rules for Abstract Notation
               One (ASN.1), International Organization for Standardization.
               International Standard 8825, (December, 1987).

          [7]  M.T. Rose, K. McCloghrie (editors), Concise MIB Definitions,
               Internet Working Group Request for Comments 1212.  Network
               Information Center, SRI International, Menlo Park,
               California, (March, 1991).

          [8]  M.T. Rose (editor), A Convention for Defining Traps for use
               with the SNMP, Internet Working Group Request for Comments
               1215.  Network Information Center, SRI International, Menlo
               Park, California, (March, 1991).






          Expires June 1994                                        [Page 53]





          draft                        UPS MIB                 December 1993


          [9]  J.D. Case, K. McCloghrie, M.T. Rose, and S. Waldbusser,
               Conformance Statements for version 2 of the Simple Network
               Management Protocol (SNMPv2), Request for Comments 1444, SNMP
               Research, Inc., Hughes LAN Systems, Dover Beach Consulting,
               Inc., Carnegie Mellon University, (April 1993).

          [10] J.D. Case, K. McCloghrie, M.T. Rose, and S. Waldbusser,
               Textual Conventions for version 2 of the Simple Network
               Management Protocol (SNMPv2), Request for Comments 1443, SNMP
               Research, Inc., Hughes LAN Systems, Dover Beach Consulting,
               Inc., Carnegie Mellon University, (April 1993).







































          Expires June 1994                                        [Page 54]





          draft                        UPS MIB                 December 1993


          8.  Security Considerations

          Security issues are not discussed in this memo.


          9.  Author's Address

               Jeffrey D. Case, Ph.D.
               The University of Tennessee
               Department of Computer Science
               107 Ayres Hall
               Knoxville, Tennessee  37996

               Phone:  (615) 573-1434
               Email:  case@CS.UTK.EDU



































          Expires June 1994                                        [Page 55]





          draft                        UPS MIB                 December 1993


          Table of Contents


          1 Introduction ..............................................    2
          2 The SNMPv2 Network Management Framework ...................    3
          2.1 Object Definitions ......................................    3
          3 Overview ..................................................    4
          4 Status ....................................................    4
          5 Definitions ...............................................    5
          5.1 The Device Identification Group.  .......................    6
          5.2 The Battery Group .......................................    8
          5.3 The Input Group .........................................   10
          5.4 The Output Group ........................................   13
          5.5 The Bypass Group ........................................   16
          5.6 The Alarm Group .........................................   18
          5.7 The Test Group ..........................................   24
          5.8 The Control Group .......................................   29
          5.9 The Configuration Group .................................   32
          6 Acknowledgements ..........................................   52
          7 References ................................................   53
          8 Security Considerations ...................................   55
          9 Author's Address ..........................................   55




























          Expires June 1994                                        [Page 56]



============================================================================

> Hello.
> This is M.Yamai.
> 
> I am Engnir. of Soliton Systems K.K. Japan.
> I plan to develop first UPS agent in Japan.
> But I  have no information about UPS MIB or UPS agent.
> Please send me the USP MIB or UPS agents information.
> 
> Regard.
> 
>  /yamai@soliton.co.jp


Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa14579;
          25 Jan 94 20:53 EST
Received: from CNRI.RESTON.VA.US by IETF.CNRI.Reston.VA.US id aa14575;
          25 Jan 94 20:53 EST
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa19486; 25 Jan 94 20:53 EST
Received: from localhost by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id UAA12430; Tue, 25 Jan 1994 20:42:49 -0500
X-Resent-To: ups-mib@CS.UTK.EDU ; Tue, 25 Jan 1994 20:42:46 EST
Errors-to: owner-ups-mib@CS.UTK.EDU
Received: from relay2.UU.NET by CS.UTK.EDU with SMTP (8.6.4/2.8s-UTK)
	id UAA12421; Tue, 25 Jan 1994 20:42:45 -0500
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: yamai@soliton.co.jp
MMDF-Warning:  Parse error in original version of preceding line at CNRI.Reston.VA.US
Received: from spool.uu.net (via LOCALHOST) by relay2.UU.NET with SMTP 
	(5.61/UUNET-internet-primary) id AAwali00641; Tue, 25 Jan 94 20:41:28 -0500
Received: from iij.UUCP by uucp2.uu.net with UUCP/RMAIL
	(queueing-rmail) id 203721.23967; Tue, 25 Jan 1994 20:37:21 EST
Received: from localhost by uucp0.iij.ad.jp (8.6.5+2.3W/2.7W)
	id JAA13591; Wed, 26 Jan 1994 09:47:04 +0900
Received: by brahma.soliton.co.jp (4.1/IIJ-U1.1)
	id AA21589; Wed, 26 Jan 94 09:32:04 JST
Date: Wed, 26 Jan 94 09:32:04 JST
Message-Id: <9401260032.AA21589@brahma.soliton.co.jp>
To: ups-mib@cs.utk.edu
Subject: subscribe


