Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa18700;
          27 Sep 95 18:10 EDT
Received: from CNRI.Reston.VA.US by IETF.CNRI.Reston.VA.US id aa18696;
          27 Sep 95 18:10 EDT
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa22240; 27 Sep 95 18:10 EDT
Received: from localhost by CS.UTK.EDU with SMTP (cf v2.9s-UTK)
	id SAA29861; Wed, 27 Sep 1995 18:04:38 -0400
X-Resent-To: ups-mib@CS.UTK.EDU ; Wed, 27 Sep 1995 18:04:36 EDT
Errors-to: owner-ups-mib@CS.UTK.EDU
Received: from cavebear.com by CS.UTK.EDU with SMTP (cf v2.9s-UTK)
	id SAA29854; Wed, 27 Sep 1995 18:04:33 -0400
Received: by cavebear.com (4.1/SMI-4.1)
	id AA01946; Wed, 27 Sep 95 15:04:29 PDT
Date: Wed, 27 Sep 1995 15:04:29 -0700 (PDT)
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: Michael Kirkham <mikek@cavebear.com>
X-Sender: mikek@pax.cavebear.com
To: UPS MIB List <ups-mib@cs.utk.edu>
Subject: Configuration Group
Message-Id: <Pine.SUN.3.91.950927145027.1887C-100000@pax.cavebear.com>
Mime-Version: 1.0
Content-Type: TEXT/PLAIN; charset=US-ASCII


Greetings folks..

I'm part of a project developing a Test Suite for testing agents 
implementing the UPS MIB (RFC 1628) that is nearing completion.  I'd like 
a little clarification about the Configuration Group:

Do the Configuration Group objects actually change operating conditions, 
or are they just basically placeholders allowing a manager to request 
values that are [likely] to be the operating values?  It seems to me that 
some of these objects could potentially be a danger to the UPS and 
equipment plugged into the UPS if they change the operating conditions.  

Specifically, upsConfigInputVoltage, upsConfigInputFreq, 
upsConfigOutputVoltage and upsConfigOutputFreq would be really *bad* 
things to change on a UPS that is in use, but MAX-ACCESS for these 
objects is read-write.  You could damage the UPS by telling it to operate 
under 110V while it's plugged into 220V, for instance.  Or you could 
damage equipment plugged into the UPS by changing its output voltage.

So, I'm a little worried about what I should be expecting the UPS to do 
when a SET is done to these objects.  The RFC doesn't say if the objects 
are not to change functional parameters when these objects are set.  It 
doesn't say they should, either.. :)

--
Michael Kirkham
InterWorking Labs, Inc.
218 Carbonera Drive, Suite 102
Santa Cruz, CA  95060-1500
Tel:  +1 408 459 9817
Fax:  +1 408 459 9768
Email:  mikek@iwl.com
WWW:  www.iwl.com




Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa07891;
          28 Sep 95 8:18 EDT
Received: from CNRI.Reston.VA.US by IETF.CNRI.Reston.VA.US id aa07886;
          28 Sep 95 8:18 EDT
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa08697; 28 Sep 95 8:18 EDT
Received: from localhost by CS.UTK.EDU with SMTP (cf v2.9s-UTK)
	id IAA10740; Thu, 28 Sep 1995 08:15:31 -0400
Received: from sun4nl.NL.net by CS.UTK.EDU with SMTP (cf v2.9s-UTK)
	id IAA10718; Thu, 28 Sep 1995 08:15:21 -0400
Received: from [193.78.6.6] by sun4nl.NL.net with SMTP
	id AA20183 (5.65b/CWI-3.3); Thu, 28 Sep 1995 13:15:11 +0100
Received: from vic1.victron.nl by vicnl.victron.nl id aa27793;
          28 Sep 95 8:37 CET
Received: from VICTRON_ONE/TEMPQ by vic1.victron.nl (Mercury 1.13);
    Thu, 28 Sep 95 8:37:55 CET
Received: from TEMPQ by VICTRON_ONE (Mercury 1.13); Thu, 28 Sep 95 8:37:34 CET
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: Jack Stiekema <JACK@vic1.victron.nl>
Organization:  Victron bv, UPS and software
To: ups-mib@cs.utk.edu
Date:          Thu, 28 Sep 1995 08:37:31 CET
Subject:       Re: Configuration Group
Priority: normal
X-Mailer: Pegasus Mail v3.22
Message-Id: <5524DF10AA@vic1.victron.nl>

> Date sent:      Wed, 27 Sep 1995 15:04:29 -0700 (PDT)
> From:           Michael Kirkham <mikek@cavebear.com>
> To:             UPS MIB List <ups-mib@CS.UTK.EDU>
> Subject:        Configuration Group

>
> Greetings folks..
Hi

> Specifically, upsConfigInputVoltage, upsConfigInputFreq,
> upsConfigOutputVoltage and upsConfigOutputFreq would be really *bad*
>
> So, I'm a little worried about what I should be expecting the UPS to do
> when a SET is done to these objects.  The RFC doesn't say if the objects

Don't worry, most of us (UPS vendors) made it Read Only.
Some have a dipswitch or jumper which allows R/W acces for localising.


Kind regards,
Jack Stiekema
Head Software Department
+------------------------+
| Phone: +31 505446284   |
| GSM:   +31 653145069   |
| Fax:   +31 505424107   |
| BBS:   +31 505446280   |
| Email: jack@victron.nl |
| WWW:   www.victron.nl  |
| Ampr:  pe0mot.ampr.org |
+------------------------+
| IMV / Victron bv       |
| Pob 31                 |
| 9700 AA Groningen      |
| Holland                |
+------------------------+


Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa15897;
          28 Sep 95 15:30 EDT
Received: from CNRI.Reston.VA.US by IETF.CNRI.Reston.VA.US id aa15893;
          28 Sep 95 15:30 EDT
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa18722; 28 Sep 95 15:30 EDT
Received: from localhost by CS.UTK.EDU with SMTP (cf v2.9s-UTK)
	id PAA22119; Thu, 28 Sep 1995 15:25:47 -0400
Received: from relay3.UU.NET by CS.UTK.EDU with ESMTP (cf v2.9s-UTK)
	id PAA22098; Thu, 28 Sep 1995 15:25:43 -0400
Received: from uucp6.UU.NET by relay3.UU.NET with SMTP 
	id QQzjej08133; Thu, 28 Sep 1995 15:25:39 -0400
Received: from stg.UUCP by uucp6.UU.NET with UUCP/RMAIL
        ; Thu, 28 Sep 1995 15:26:07 -0400
Received: by mcbain.stg.com (4.1/SMI-4.1)
	id AA22870; Thu, 28 Sep 95 14:00:14 CDT
Date: Thu, 28 Sep 95 14:00:14 CDT
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: Chris Herzog <stg!zog@uunet.uu.net>
Message-Id: <9509281900.AA22870@mcbain.stg.com>
To: uunet!CS.UTK.EDU!ups-mib@uunet.uu.net, 
    uunet!cavebear.com!mikek@uunet.uu.net
Subject: Re: Configuration Group

> I'm part of a project developing a Test Suite for testing agents 
> implementing the UPS MIB (RFC 1628) that is nearing completion.  I'd like 
> a little clarification about the Configuration Group:
> 
> Do the Configuration Group objects actually change operating conditions, 
> or are they just basically placeholders allowing a manager to request 
> values that are [likely] to be the operating values?  It seems to me that 
> some of these objects could potentially be a danger to the UPS and 
> equipment plugged into the UPS if they change the operating conditions.  
> 
> Specifically, upsConfigInputVoltage, upsConfigInputFreq, 
> upsConfigOutputVoltage and upsConfigOutputFreq would be really *bad* 
> things to change on a UPS that is in use, but MAX-ACCESS for these 
> objects is read-write.  You could damage the UPS by telling it to operate 
> under 110V while it's plugged into 220V, for instance.  Or you could 
> damage equipment plugged into the UPS by changing its output voltage.

I think you're mixing what the MIB allows with the real world more than you
might need to as far as a test suite goes.  My feeling is that you're right in
testing all the way up to the full capabilities of the MIB -- including
changing these values to possibly non-sensical combos.  If the MIB allows
writing, test that bad boy for writing!

For a test suite, you should test writability of any object that the MIB
defines as writable but then need to interpret the entire set of results in
the view of the various conformance levels.  Different agents could conform
to different levels which would affect how certain objects operate (or in fact
if they are supported at all) -- the MIB states that R/W access is not
_required_ but certainly is _permitted_.  So long as you keep in mind the
intended level of conformance when you report the results at the end of the
test, things should be cool.  These are just some particular objects where if
you only allow read access you're OK, but if you actually do allow write access,
you aren't any "more" correct than a read-only implementation IMHO.

Like Jack pointed out, I think the mfgrs have taken a precaution or two to
stop "bad" things from happening if in fact they allow write access to those
variables so you certainly should "test" them for writability.  If setting a
variable causes the UPS or it's load to explode; well, let's just say it's
more than an agent conformance problem :o


> So, I'm a little worried about what I should be expecting the UPS to do 
> when a SET is done to these objects.  The RFC doesn't say if the objects 
> are not to change functional parameters when these objects are set.  It 
> doesn't say they should, either.. :)

I think you'd be safe to assume that if you _can_ write those values, you
actually changed the operational parameters.  Otherwise the implementation is
reporting bogus data if it's just using it as a "placeholder".


Just my thoughts...




zog


--

Chris Herzog					Software Technologies Group
zog@stg.com


Received: from ietf.nri.reston.va.us by IETF.CNRI.Reston.VA.US id aa19641;
          28 Sep 95 18:17 EDT
Received: from CNRI.Reston.VA.US by IETF.CNRI.Reston.VA.US id aa19637;
          28 Sep 95 18:17 EDT
Received: from CS.UTK.EDU by CNRI.Reston.VA.US id aa22693; 28 Sep 95 18:17 EDT
Received: from localhost by CS.UTK.EDU with SMTP (cf v2.9s-UTK)
	id SAA11925; Thu, 28 Sep 1995 18:11:27 -0400
Received: from relay1.UU.NET by CS.UTK.EDU with ESMTP (cf v2.9s-UTK)
	id SAA11911; Thu, 28 Sep 1995 18:11:22 -0400
Received: from uucp3.UU.NET by relay1.UU.NET with SMTP 
	id QQzjeu12536; Thu, 28 Sep 1995 18:11:09 -0400 (EDT)
Received: from peernet.UUCP by uucp3.UU.NET with UUCP/RMAIL
        ; Thu, 28 Sep 1995 18:11:13 -0400
Received: from dorothy.peer.com by peernet.peer.com (4.1/SMI-4.1)
	id AA05598; Thu, 28 Sep 95 15:07:46 PDT
Received: by dorothy.peer.com (4.1/SMI-4.1)
	id AA12793; Thu, 28 Sep 95 15:07:48 PDT
Date: Thu, 28 Sep 95 15:07:48 PDT
Sender:ietf-archive-request@IETF.CNRI.Reston.VA.US
From: Randy Presuhn <randy@peer.com>
Message-Id: <9509282207.AA12793@dorothy.peer.com>
To: ups-mib@cs.utk.edu
Subject: Re: Configuration Group

Hi -

> Date: Thu, 28 Sep 95 14:00:14 CDT
> From: zog@stg (Chris Herzog)
> To: CS.UTK.EDU!ups-mib@uunet, cavebear.com!mikek@uunet
> Subject: Re: Configuration Group
...
> I think you'd be safe to assume that if you _can_ write those values, you
> actually changed the operational parameters.  Otherwise the implementation is
> reporting bogus data if it's just using it as a "placeholder".
...

There's some interesting work going on with EWOS (European
Workshop for Open Systems) PT (Project Team) 28 on the
testability of managed objects.  If you ask nicely, you may
get a draft from John Westgate <100014.1305@compuserve.com>
when the next revision goes out for comment.

This work addresses issues like the ones in this discussion.
ISO/IEC JTC1/SC21/WG7 is considering using the PT 28 work and
will discuss it in Kobe, Japan in November.  If you have
comments you'd like included, contact me for ways of getting
them into X3T3.

 ---------------------------------------------------------------
  Randy Presuhn                 PEER Networks, Inc.             
  Voice: +1 408 556-0720        1190 Saratoga Avenue, Suite 130
  Fax:   +1 408 556-0735        San Jose, California 95129-3433
  Email: randy@peer.com         USA                             
 ---------------------------------------------------------------
